what is dry leg and what is wet leg?
Answers were Sorted based on User's Feedback
Answer / santosh nanavati
We are doing the impulse tubing work on HP &/LP side DP
transmitter for level measurement of atmospheric close or
open vessel as per the process application. If the LP side
of tubing is filled with suitable fluid (water or process
fluid), it is called wet leg. Under this circumtances, the
transmitter zero condition will be towards negative
pressure range equivalent to the pressure head of filled
fluid in the LP side tubing. Vice versa if side of tubing
is not filled any fluid & kept empty i.e.dry, it is called
as dry leg. Under this condition,the transmitter zero
condition will not be towards negative pressure range.
Is This Answer Correct ? | 16 Yes | 3 No |
Answer / sabry
If the impulse line connected to the low side of the differential pressure instrument is filled with a suitable fluid, it's called (wet leg).
If the impulse line is empty, it's called (dry leg).
Dry leg & Wet leg is a technique used in differential pressure measuremnt for 2 main reasons:
1 - We use (wet leg) to prevent the dangerous fluid from harming the sensitive instrument.
2 - In closed tank application, we use (wet leg) to prevent vapour condenstion due to temperature variation, so we get a stable/accurate measurement.
Good Luck
Ahmed Sabry
I&C Senior Engineer
Cell:+2 (0122) 1367310
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / ranish
Generally dry leg means without water ex: temperature
measurement thermo meter with out cloth or shield directily
to atm and with cloth ( we want to make it wet for
measurement)and subjected to atm or process
by ranish
Is This Answer Correct ? | 0 Yes | 9 No |
control panel design guidelines
how commission a transmitter evev plant is already running
what is meant by control valve sizing?
what is the different between plc and dcs ? I know full name of this two but I want to know what structure and working style and speed I/O capacity and controller difference?
What is Difference between Bench Set & Operating Range of Control Valve?
Before erect the instrument what should you do?
what is difference between profibus and field bus?
why magnetic flow meter is not used in thermel power plant operation
given a processor batch of 1000 resistors moving on the conveyor belting in a large factory. the resistors is value at 10k ohms each but when the resistors reach the quality control, some of the resistor has been rejected caused by failure in manufacturing.the high quality measurement is used to determine the failure. describe the instrumentation terminology in measurement of a system above with explaining the important in:- -reliability -sensitivity -repeatability -precision -range -resolution -linearity -hysteresis -error -accuracy (answer must related to the scenario above)
WHY THE DEGREE OF VALVE PLUG AND VALVE SEAT IS SLIGTLY DIFFERENT I CONTROL VALVE TRIM DESIGN
how will you check torque value during Factory acceptance Test for control valve/ESD ON/OFF VALE how will you confirm this torque value is being correct, Which document will you be refer.
principle of automatic votage regulator