What is Difference between Bench Set & Operating Range of
Control Valve?
Answer / praveen kumar
bench set is called based on the line pressure, control valve actuator spring adjustment....if control valve spring range 0.4-1.0 bar means ..the control valve will start to opened at 0.4bar instrument air pressure.before or after 0.4bar it should not start to open, at 1.0 bar the valve should be fully open(max travelling range of valve)...
Operating range is called as positioner output 0.2 to 1.0 bar...
Is This Answer Correct ? | 1 Yes | 0 No |
i need some objective type questions in instrumentation
How to Calibrate Vibration Probe (Axial, Redial) in field
How to Calibrate Temperature Switch in field
What is sensitivity of K type thermocouple? Is polarity important in thermocouple connections?
what is the pressure in the tank when its level of liquid is 1.5 meters when its total capacity is 2 meters
How does temperature bath work? How does coil gets heated only by applying some current?
0 Answers Process Control Technologies,
in the construction field why hook up s.s.tubing for transmitter using upto 6mtrs of closed loop, but y not open loop nomore restriction
What is PLC(programmable logic control)?
different between calibration range and instrument range ?
How d.p. Transmitter can be applied to open tank?
what is the principle of vibration
in valve is constructed as per SME B 16.34, then which standard is used for fire testing of valve?.