how commission a transmitter evev plant is already running
Answers were Sorted based on User's Feedback
Answer / ashish namdev, bina refinery
when plant is running that time any Tx can be commission but
few precautions need to follow-
1. all interlocks which is related with Tx to be checked &
put it in bypass.
2. Check all process parameters in field.
3. If these all conditions are healthy then Tx can be lineup
or commission.
4. Check all settings, ranges etc.
5. After commission Tx interlock take in line.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sam
1) Check whether the transmitter is in closed loop or not.
2)If it is in closed loop, then do the engineering login
from your server and force the current value.
3)Then come to field isolate the transmitter from the
process , open the vent make the transmitter entirely free
from process and see whether the transmitter is having the
zero error or not
4)If it is not having the zero error then make flush out the
impulse lines and take the transmitter in line
5)If it is having the zero error then do the zero
calibrstion from ur HART communicator by selecting online mode.
6)Observe the transmitter for 5 minutes then remove the
force and put the transmitter in closed loop.
| Is This Answer Correct ? | 2 Yes | 0 No |
i hav applied for the post of engg. in iocl so please require the past test papers fro instrumentation engg please please help me and send me the papers or tell me the pattern and type of ques asked in examination......
what is the responsibility of an instrument commissioning supervisor
what is concept of field,control room area in transmitters?
what is the difference between two wire transmitter and 4- wire transmitter
where do you give the 4-20 ma i/p in a MIL control valve?
what is exact time to study dcs and plc cources
what is Best Among SINK Or SOURCE Type Design In Digital Signal, Either Iput Or Output? WHY?Can any one..
Why even multiple power supplu r used in instrumentation system?
what is orfics working in main steam line. is it increase pressure, velocity of steam flow and dicrease steam flow rate. or any other
we have level transmitter for h2s04 storage tank capacity 10k ,always there are failure of transmitter due to failure of magnetic floats ,please come up with solutions at the earliest.
why we use cascade control and feed forward control in 3 element drum level control measurement of steam drum .what is cascade and feed forward control system ?give example .
units of pressure,flow, level,temperature? principle of pressure gauge? calibration of pressure tx., level tx., temperature tx.flow tx.? description of two wire ,three wire and four wire R.T.D.? WHAT IS INPUT AND OUTPUT OF TX.? WHAT IS INPUT AND OUTPUT OF R.T.D. AND THERMOCOUPLE? WHAT IS HOT LOOP AND COLD LOOP? WHAT IS INPUT AND OUT PUT AND OUTPUT OF D.C.S. AND P.L.C.? PRINCIPLE AND WORKING OF HART? WHAT IS PNP AND NPN PROXY? CALIBRATION OF PRESSURE ,LEVEL ,FLOW SWITCH? DESCRIPTION OF FIELDBUS FOUNDATION? WORKING OF SOV.?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)