why is the vector group analysis done in transformer tests
Answers were Sorted based on User's Feedback
Answer / ganeswar sahu
To check the phase angle displacement between two
windings of a manufactured traformer and to check whether
internal winding connection is matching to the vector group
as mentioned in the name plate .
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / raju.t
1. To check the phase angle displacement between two
windings of a manufactured trafo.
2. To check the correctness of vector group mentioned in
the name plate of trafo and actual connection.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / jagdish krushnarao zeliye
vector group of transformer is used to know the phase angle
for parallelling operation
| Is This Answer Correct ? | 13 Yes | 5 No |
Answer / saba anjum
vector group are made to know at what position the secondary
winding of transformer we get star and delta voltages . and
it indicates the type of winding in primary and secondary
which helps in parallel operation of transformer with
different ratings having same vector group .
| Is This Answer Correct ? | 13 Yes | 7 No |
Answer / purav solanki.
for the parallel operation of two transformer.
| Is This Answer Correct ? | 13 Yes | 8 No |
Answer / usama badran ali
vector group analysis used for two important things?
1-it describes the charcteristic of transformers...how?
1-primary and secondary connections.
2-low and high voltage sides.
3-leading angle between high and low voltages.
2-to connect two parallel transformer, you should know the
line to line voltages of two transformer (i mean each
similar line voltages of the parallel transformers ).
3-in the modern technolgy of power electronics in three
phase inverters i can eleminate fixed order of harmonics by
changing the transformer connection .
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / saksh
to check the phase angle displadement so as to know the
power factor itis lag or lead
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / kulu
TO Check the phase displacement between HV winding and Lv
winding
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / ramama
for parallel operation of two different rating transformers
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / ganesh nayak
Vector anlysis is done to check whether the transformer
under test is suitable for parallel operation with another
transfomer having same vector group and voltage ratio but
difference in KVA rating.And to know the phase displacment
and polarity of the transformer.
| Is This Answer Correct ? | 2 Yes | 1 No |
what could be the RMS value and average value of a 4 phase sine wave?
how the testing of protection CT Testing done through Primary injection kit please describe in detail procedure...
Difference between SFU & FSU with advantantages & drawback?
how to calculate single phase motor efficiency ?
What is oscillator circuit?
If the output of a 100kva, 415v generator is stepped up to 11kv with a 500kva transformer,can the transformer be Loaded above the source generator loading?
Why we use mostly circular coil in transformer? not square or rectangular type of coil.
what is the difference between ups & inverter
4 Answers Cushman Wakefield, Dana Group,
WHY IS THE SIZE OF HOLE OF THE EARTH POINT IN THE PLUG POINT BIGGER THAN PHASE AND NEUTRAL
If auto trip is operated, can you close the breaker.
what happen when dc supply is given to the transformer
control wiring purpose,standards, ferrule code standard, interlock, schematic, symbol
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)