why is the vector group analysis done in transformer tests
Answer Posted / joe callaghan
Transformer vector relationship is tested by shorting the
primary A phase to secondary A phase, then applyying a
three phase voltage to the primary side of the transformer.
Voltage measurements are then taken as follows:
A-B
B-C
C-A
B-b
C-b
B-c
C-c
These values will then allow you to draw the vector diagram
of the transformer.
Is This Answer Correct ? | 32 Yes | 9 No |
Post New Answer View All Answers
how electrical earthing maintenance done in industry?
is that any software calculator to calculate the size of cable
what are symmetrical and non symmetrical components in electrical installation.
how to calculate the tarriff for an industry whose kva demand is 10 mva
What is the RME and explain the full form and what is the RME work?
What the formula for calculating no.of earthings & size of earth strip for 100mX90m shop.
How to decide the size of the capacitor for a single phase induction motor say 2 HP ??
What will happen if we on 200kvr capacitor bank(11kv in bus)If there is low load on transformer (1.5 mva 33/11 kv)
Define conversion efficiency of a power amplifier.
What are the necessary components of the feedback control system?
defult setting in p220 micom motor proction relay for 11kv,640kw,f.l.a.-40a,1440rpm ht motor?
In India the supply voltage is 230 volt A.C. During the negative half cycle phase becomes neutral and neutral become phase? or what will happen during negative half cycle? how the electrons flow during positive and negative half cycle?
Explain about how is it working Earth fault'relay and wahts the resistance value of earth bed
The principle of switching circuits for different types of batteries in application of storage systems
Percentage losses in power generation?