How to select the cable size for the given load ?Pls
explain the Formulae
Answers were Sorted based on User's Feedback
Answer / sree
presuming, the unit of load is in HP(It is out put power)
output in KW= 735.5xHP(A).
Input in KW= A/Effy.(B).
Current= B/((1.732 * V * 0.7) (for 3 Phase star connected
load)(C)
Starting current= (1.5 to 2 times of full load current
(approx.)(D)
Based on cable catalague the size of cable will be chosen
as per above current rating(D).
or
Presuming the load is in KW(It is input power)
current=KW/((1.732 * V * 0.7) (for 3 Phase star connected
load)(A).
Starting current= (1.5 to 2 times of full load current
(approx.)(B)
Based on cable catalague, the size of cable will be chosen
as per above current rating(B).
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / vinay
Depending on amps rating.
A=P/V (for 1phase. P=Power in W, V=Voltage)
A=P/(1.732 * V * 0.7) (for 3 Phase)
Is This Answer Correct ? | 6 Yes | 7 No |
Answer / jagjeet
Dear Mannu/ Vinay
Efficiency has to be considered for the system also.
Is This Answer Correct ? | 1 Yes | 4 No |
is earthing is necessary if we use armoured cable
1 Answers ABB, Schwing Stetter, Siemens,
why in transformer there is not rotating fiddl/ magnetic field like motor
Dears we deal in Chemical are Plate earthing. Kindly call if any requirement and questions. Tech Earth Solutions Mohit Verma 8791071007
expansion of rccb
why we can not use dc in our country( INDIA)
Difference Between Differential Relay and Restricted Earth Fault Relay of Power Transformers
What is the settings of distance protection relay in 400 kv line
Ohms law explain
send me any model test paper of clerical post of state bank of india.......
Application wise, where we should use AC motors and where we should DC motors?
1.difference between sts & ats? 2.what is fm200 system brefly explain?
Why is it that bus reactors are not accompanied by a neutral grounding reactor whereas a line shunt reactor is? PGCIL does so.