How to select the cable size for the given load ?Pls
explain the Formulae
Answers were Sorted based on User's Feedback
Answer / sree
presuming, the unit of load is in HP(It is out put power)
output in KW= 735.5xHP(A).
Input in KW= A/Effy.(B).
Current= B/((1.732 * V * 0.7) (for 3 Phase star connected
load)(C)
Starting current= (1.5 to 2 times of full load current
(approx.)(D)
Based on cable catalague the size of cable will be chosen
as per above current rating(D).
or
Presuming the load is in KW(It is input power)
current=KW/((1.732 * V * 0.7) (for 3 Phase star connected
load)(A).
Starting current= (1.5 to 2 times of full load current
(approx.)(B)
Based on cable catalague, the size of cable will be chosen
as per above current rating(B).
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / vinay
Depending on amps rating.
A=P/V (for 1phase. P=Power in W, V=Voltage)
A=P/(1.732 * V * 0.7) (for 3 Phase)
| Is This Answer Correct ? | 6 Yes | 7 No |
Answer / jagjeet
Dear Mannu/ Vinay
Efficiency has to be considered for the system also.
| Is This Answer Correct ? | 1 Yes | 4 No |
Details about Flux Compensated magnetic Amplifer starter for motors
what is the differnce between high impedance relay and low impedance relay
how do you select the ct/pt rating in substation
1 Answers Apollo, Shreem Electric Ltd, Tata Motors,
draw the full wave and half wave circuit of 3 phase system and inverter circuit used in ups
In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours, what would be result of this condition?
19 Answers Essar, GAIL, Vizag Steel,
what is the difference between 4pole & 6pole DC Motors & give advantage ?
difference between servo motor and synchronous motor
what is advantage in open delta connection?
what is the use of providing earthing for tanks? i know for lightning we use earthing ? Here one of my ONGC project there is no need of lightning protection and there is no power connection near by tank in that situation also ONGC asking earthing for tanks but we didn't understanding why they asking earthing? is anybody tell exact answer?
why ht line fuse wire is so thin
what is impedence voltage
one hp 3phase motor what generate power factor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)