Answer / balaji
1. Preparation (Permit to work)
2. Separation (Trip the Breaker)
3. Isolation (Isolator isolates)
4. Earthing & Short circuit (Earthing)
5. Screening & Marking the area (Barricading the work area)
Is This Answer Correct ? | 11 Yes | 2 No |
Answer / manzoor hussain
1)First need to obtain isolation permit(work permit)
2)Confirm substation no., breaker no.
3)Inform to control engineer
4)Transfer the load from LV side
5)First need to trip the vcb(electrically or manually)
6)Disconnect DS switch (isolator)
7)Need to close the earth switch (ES)
Is This Answer Correct ? | 0 Yes | 0 No |
what is the purpose of supervision relay coil
we touch other end of the tester supply, why do not get shock?
What will hapen if we connect more capacitors than required for powerfactor control? Exactly what will be the effect on power system?
What are the properties of a resistor?
CT Ratio of a energy meter connection is Red Phase : 100/5A, yello Phase : 50/5A & Blue phase : 100/5 A what is the overall Multiplication factor
how much load 15kva dg set can bear
Generally at what power factor the electronic equipments like computer, TV, EPABX etc.,operates. Please tell me.
How to check phase R,Y,B
can u give me a brief idea about power line carrier communication ??
If breaker is undefined position, first step to do.
What is the use of Isolation Transformer, and Neutral is using for return path, finally this current is going.... but same time the voltage of the neutral should be below 1 V...
what is diff. b/w of earth & neutral?. why we are separately using ?