Answer / balaji
1. Preparation (Permit to work)
2. Separation (Trip the Breaker)
3. Isolation (Isolator isolates)
4. Earthing & Short circuit (Earthing)
5. Screening & Marking the area (Barricading the work area)
| Is This Answer Correct ? | 11 Yes | 2 No |
Answer / manzoor hussain
1)First need to obtain isolation permit(work permit)
2)Confirm substation no., breaker no.
3)Inform to control engineer
4)Transfer the load from LV side
5)First need to trip the vcb(electrically or manually)
6)Disconnect DS switch (isolator)
7)Need to close the earth switch (ES)
| Is This Answer Correct ? | 0 Yes | 0 No |
how to calculate voltage regulation?
What happen if 200 KVAR capacitor connected to power continuesly?
Is it advantages of having star-delta vfd than normal star vfd , if yes why?
how we can produce negative DC voltage ? please explain it .,thank u
HOW EFFICIENTLY LOAD IS SHARED BETWEEN ALTERNATORS
What are armoured cables?
Where the Dry type tranformers are used.
Seamless tubes are made by?
how many units (kwh) are there if in one MW?
how to calculate relay rating for 50kw load
What are the different types of hydro schemes?
difference between the earthing,grounding and neutral
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)