Sir,
why generating power plant operating at above 0.9 lag?
detail explaination?
Answer / sanu chaudhary
armature current of alternator depends upon the power
factor of machine .AT THE UNITY POWER FACTOR armature
current is minimum ,armature current of machine will
increse for same power if power factor of machine is
lagging as well as leading so it is desired to run the
machine near the unity power factor for optimum utilisation
of capacity of machine .in the leadind power factor machine
take reactive power from the infinte bus or grid and
machine is under excitation so it may be the cause of
panelty from power corporation due to reaciving of reactive
power hence we operate the machine near .9 lagging power
factor
| Is This Answer Correct ? | 8 Yes | 4 No |
We have drive feeding an output contactor for a 5000 hp motor @ 5kV application. The motor FLA is 629amps x 1.25% service factor = 786.25 amps The cable that we current have in place between the drive and the output contactor is 350kcmil- MV-105 (parallel cables). Per the NEC table 310.60 (C) (69). This show the cable ampacity is at 615 amps per cable for a rating of 1230 amps. We have derated the cable for the cable tray and the multiple cables application and our calculations show that after the correction factor factor we are at 922amps. 1230 amps x .75% correction factor factor = 922.5 amps. The customer is driving us to then use another safety factor of .25% off of the already derated cable. Can you please provide a longhand calculation for your solution on this application?
What is the function of semicon in 33kv ht cable ?
why two point starter,three point starter, four point starter cannot be used for A.C machines?
What is meant by the KA-rating of a circuit breaker? In this regard, discuss the stresses experienced by the circuit breakers
what is the difference between thermal magnetic release and microprocessor based release breakers. what are the advantages of latter over the first one...
5 Answers Jackson, Karthik Industries, McD BERL, TCS,
How Size of Busbar is determined for a particular load.
Explain the power rating of a bulb, say 60W, what if the voltage changes
along with technical test papers
why substation rating interms of 11 multiples???like 11kv/33kv iis there any special reason???
What are the advantages of D.O.L Starter in 3 phase induction motor?
what the purpose of data retrivala panel in substation
What is Servo Ventilated Motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)