What is the function of semicon in 33kv ht cable ?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
It is used to influence the electric field within the
insulation layer.The semicon layer has to removed at the
termination at least 6-9 inches below the lugs ,as
otherwise there will be short circuit along this layer.As
this layer is not doped, you have to treat it as a conductor.
Is This Answer Correct ? | 10 Yes | 4 No |
Answer / paramesha r l
Purpose of semiconducting layer is to maintain uniform distribution of Poynting vector i.e., P=ExH in insulator or otherwise power P=EXH densely concentrated at insulation point where two phase are comes in contact.
what Semiconducting layer does is equipotential over outer surface of insulating medium as it is like a free space.
Semiconducting layer needed to remove at termination i.e, 35 to 50 cm from lugs point.
If semiconducting layer not removed at termination leakage current flows between conductor to semiconducting which is hardly a distance of 5mm at eventually it fails.
Is This Answer Correct ? | 0 Yes | 0 No |
The purpose of Semi conducting tape is only to transmit the
heat from insulation to cu. tape over it. this heat is
produced in Core due to flow of current. Further, to
TERMINATE THE CABLES, ALL CONDUCTING AND SEMICONDUCTING TAPE
IS REMOVED FROM INSULATION AS current in cable can also come
into insulation and it may be damage the cable, dangerous to
persons working.
Is This Answer Correct ? | 3 Yes | 9 No |
Answer / marlo
Usually HV cable has a semi conducting, one purpose it to protect your connected load in severe damage and the system as well. In the case of unexpected faults along with this cable,any small leakage current detected will trip its protection.
Is This Answer Correct ? | 2 Yes | 10 No |
Is it weather conditions make any problems to the electrical equipments and if yes means is it any precautions needed?
What is the effect on in Zone and out zone fault if Phase side CT is Vk/2<30 mA and Neutral side is CT is Vk/4<30 mA for Transformer REF protection
what is the excess air in furnace
What are the steps for Testing of 6.6KV HT Panels?
Question about ct secondaries connections?
A group of machines (wind turbines) connected with 33KV feeder and each machines are having individual VCB. The 33KV feeder connected with 110KV/33KV substation. The 33KV feeder tripped by over current at Substation and fault recorded at Substation as OC-R&Y phase. Same time the group of machines VCB tripped by over voltage, the fault recorded voltage was above 66KV by numerical Under/Over voltage relay. While grid drop time, this much of voltage hike is possible?
How to calculate multiplication factor in kva example 500kva ans pls ?
how can decide the current rating of oltc
How much amperes needed for starting of 4HP motor?
How i measured Bus bars weight without wighting ?
in india why 50 hz and 220 volt taken as standard rating for equipments whereas in US 100hz and 110v is consided as standard rating.is this method save power.
pls tell what are doing the three phase motor star and delta connetion with circuit diagram and control wiring .