What is the function of semicon in 33kv ht cable ?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
It is used to influence the electric field within the
insulation layer.The semicon layer has to removed at the
termination at least 6-9 inches below the lugs ,as
otherwise there will be short circuit along this layer.As
this layer is not doped, you have to treat it as a conductor.
Is This Answer Correct ? | 10 Yes | 4 No |
Answer / paramesha r l
Purpose of semiconducting layer is to maintain uniform distribution of Poynting vector i.e., P=ExH in insulator or otherwise power P=EXH densely concentrated at insulation point where two phase are comes in contact.
what Semiconducting layer does is equipotential over outer surface of insulating medium as it is like a free space.
Semiconducting layer needed to remove at termination i.e, 35 to 50 cm from lugs point.
If semiconducting layer not removed at termination leakage current flows between conductor to semiconducting which is hardly a distance of 5mm at eventually it fails.
Is This Answer Correct ? | 0 Yes | 0 No |
The purpose of Semi conducting tape is only to transmit the
heat from insulation to cu. tape over it. this heat is
produced in Core due to flow of current. Further, to
TERMINATE THE CABLES, ALL CONDUCTING AND SEMICONDUCTING TAPE
IS REMOVED FROM INSULATION AS current in cable can also come
into insulation and it may be damage the cable, dangerous to
persons working.
Is This Answer Correct ? | 3 Yes | 9 No |
Answer / marlo
Usually HV cable has a semi conducting, one purpose it to protect your connected load in severe damage and the system as well. In the case of unexpected faults along with this cable,any small leakage current detected will trip its protection.
Is This Answer Correct ? | 2 Yes | 10 No |
Is vtg is controlled by the resistor? if else how much?
What is the min.& max distance between two earth spikes is required for measuring earth resistance of an earth pit? Is the manufacturer of Earth tester decides this? Pls explain.
11KW Delta motor is taking about 44Amps in star and goes upto 70Amps in delta and trips OFF. The rated current is 26Amps. Application is for the blower. The motor takes ( no load without coupling impller ) only 2.5A and 5Amps in star & delta starter test.Need to know why its taking high current.
What is SF6 Circuit Breaker?
What is class X ct? What rare its uses?
differentiate PLC,DCS,SCADA?
what are the causes for strip heater failure ?
generally rectifying of ac tells. ac signel appear at phase and neutral with respect to frequency by -veand +cycles. but we doesn't experience shock with neutral in house hold ac??????.
i have 1500 kva generator how much maximum load avilable of use
n1 =1000 n2 =?;v1 =200:v2 =400
WHEN I AM CONNECTIN TWO ELCB IN PARALLEL.ONE ELCB TRIPPED...HOW IT HAPPEND??
WHAT IS NORMAL VECTOR GROUP USED FOR DESIGNING OF TRANSFORMERS??