We have drive feeding an output contactor for a 5000 hp
motor @ 5kV application.
The motor FLA is 629amps x 1.25% service factor = 786.25
amps
The cable that we current have in place between the drive
and the output contactor is 350kcmil- MV-105 (parallel
cables). Per the NEC table 310.60 (C) (69). This show the
cable ampacity is at 615 amps per cable for a rating of
1230 amps.
We have derated the cable for the cable tray and the
multiple cables application and our calculations show that
after the correction factor factor we are at 922amps.
1230 amps x .75% correction factor factor = 922.5 amps.
The customer is driving us to then use another safety
factor of .25% off of the already derated cable. Can you
please provide a longhand calculation for your solution on
this application?
No Answer is Posted For this Question
Be the First to Post Answer
what is the difference between LT & HT Motors
how to calculate transformer turn primary & secondary side 11kv to 420v
What are the different types of cable jointing methods for HT and LT power cable?
how to find out this one mcb r mccb?
Block diagram of Power line communication?
what is the impedence
what is diffrances between fuse and breaker protection? which one is best?
How to connect the chemical earthing and complete process tell me plz
AT THE TIME OF INSTALLING THE POWER PLANT POWER IS TAKEN FROM NEARBY GRID AND GIVING THE SUPPLY TO THE GENERATOR WHICH ACTS AS MOTOR. WHAT IS THE NEED OF RUNNING THE GENERATOR AS MOTOR?
Getting nusense tripping in a 11KV soft starter, have checked all it control supply & contactors but did not get any fault please help.
What is an Automatic Voltage Regultor & what is its use? What are the general componets we use to design an Automatic Voltage Regulator..What are the factors to be considered for its design?
Motor and transformer working with same principle so why motor rotates while transformer not?