What is a PID controller and how can it to applied to our
everyday life?
Answers were Sorted based on User's Feedback
Answer / waqas ali
A PID controller is composed of three components:
P - Proportional
I - Integral
D - Differential
It controls the overall response of a system. The "P" term
controls the gain of the system. The "I" term controls
error and "D" term controls the overshoot of the system.
| Is This Answer Correct ? | 28 Yes | 3 No |
Answer / www.islamqa.com
Actually we can make it simple:
# P:
it's a controller gain which modify the controller o/p
proportional to the error.
# I:
it's a controller gain which modify the controller o/p
proportional to the integral of the error.
# D:
it's a controller gain which modify the controller o/p
proportional to error rate of change.
We have 4 parameters in our control loop to focus on:
1 - the rise time: the period of time during which the pv
get 90% of the desired sp value
2 - max overshoot
3 - settling time: the period of time during which the pv
get the desired sp value and saturate.
4 - error/offset
we can get it clear from this pic:
http://controls.ame.nd.edu/ame437/S2003/hw1/specifications.j
pg
Now we will take a look about the effect of each controller
gain on these parameters:
# P gain:
decrease rise time
increase max.overshoot
increase settling time
decrease error (but not eliminate)
# I gain:
decrease rise time
increase max.overshoot
increase settling time
eliminate error.
# D gain:
no effect on rise time
decrease max.overshoot
decrease settling time
decrease error.
the previous is guidelines to be in background while
dealing with PID,but they are not sharp limits.
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
ahmedsabry.online@gmail.com
CELL.: 00 2 0121367310
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / ajith294
At first you should understand what is the controller.
A controller is the device in a closed loop, that compares the measured valve (actual valve) with the desired valve and calculate the out put manipulated variable. Then The time (T) responds is determined by P,I,D
P: manipulated variable our put is proportional to the system deviation. that means variable only present if there is any system deviation.
I: manipulated variable is continues to increase, the system deviation decreases. this process continuous until system deviation is zero.
D: Differential compound evaluate the speed of change of the system deviation.
so if using the PID controls, we can control the flow to our desired valve at a very short time.
Best Regards
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / basheeruddin
PID controller is use to correct the errors between measure value PV ( i.e process value ) and set piont (sp).
| Is This Answer Correct ? | 4 Yes | 1 No |
Rtd sensor how to calibrate
In bimetallic temp. Gauges why does metal strip bend? Why do we use low expansion factor metal and high expansion factor metal in bimetaliv strip?
1 Answers Process Control Technologies,
Describe how to use megger to measure the earth resistance and insulation resistance
pressure switch range 0 to 2bar.i have to install from ground level to 5 meters height.what is the formula the to increse the range ? and every 1 meter how much pressure should be add ?
why we are using negative range like -750 to 0 mmwc in closed tank?and what is the reason can you explain clear?
what is difference between pressure,flow and level control valve.
what are the programming languages used in dcs
My question may be very basic or childish but this question still persists in me, someone plz help me 1.why do we go for differential equations to analyze a system? 2.why do we solve it using matrices, is there any specific reason for using matrices other than the stories like it is simple,faster etc.
IF PLC POWER FAILURE THEN WHAT HAPPEN?
Question on maha cement
My flow transmitter range is 0-1000mmwc.DCS range is 0- 100m3/hr.What is correspond out put in terms of milliamps if my flow is 65m3/hr
Level in tank under vacuum (Ex: Condensate Tank of Power Plant)is measured using D. P. type level transmitter. Tank is subjected to vacuum of 755mmHg. Is it possible to fill wet leg ( i.e. leg connected to top of vessel with low point of D. P. xmtr) with water?. Are there chances of water getting sucked under vacuum? if yes, what is the solution?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)