My flow transmitter range is 0-1000mmwc.DCS range is 0-
100m3/hr.What is correspond out put in terms of milliamps
if my flow is 65m3/hr
Answers were Sorted based on User's Feedback
Answer / krishnakumar k
flow meter range 0-100m3/hr will give output 4-20ma
for 65m3/hr output is = {(16/100)*65} + 4
=14.4ma
Is This Answer Correct ? | 18 Yes | 5 No |
For 0 m3/hr- 4mA
for 100 m3/hr- 20mA
for 65 m3/hr- 14.4 mA
Is This Answer Correct ? | 9 Yes | 9 No |
in instrumentation why we are using 4-20mA , why not voltage ? if somebody design a instrument which works on voltage then can we use that instrument?
what is mean by hot loop and cold loop testing, whts different between both
On LPG sphere tank we used LIT for level indication.High side port is connected to the bottom of the tank while low side port connected to the top. I would like to know how to fill the glycerin on its low side with two condensing pot installed,one from top and the other one for its drain line.Please I need your expertise...thanks
how can calibrate vacume trasmitter by HART COMMUNICATOR ?
what is the procedure of O2 analyser calibration?
what is the full form of psig.
What is purpose of shield wire?
What pressure transmitter.
Explain why use mmwc unit?
what is modbus?and why use it?what benifit
what is the procedure for auto tune in masoneialn 12300 series displacer type transmitter?
What are the two states of a controller