why transformer ratings in kva?
Answers were Sorted based on User's Feedback
Answer / princealekota
Since transformer is a static there will not be any
rotational losses it have only iron loss depend upon
voltage and copper loss depend upon current
for AC supply systems like generator, transformer rating is
done in KVA because of inductance present in AC . we don't
know load is resitive or inductive
so we will take load KW=KVA,
power = voltage*current*cos(pi)
if load isinductive cos(pi) have some value less than 1
if load is resistive cos(pi)is 1
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / karthik
Basically any rotating machine depends up on power factor
and other rotational losses. Transformer is not a rotating
machine and transformer losses depends on only Iron losses &
Copper losses. Iron losses depends on voltage and Copper
losses depends on current. these losses not depends on power
factor. So Transformer rating measured in KVA.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / purushotham
In transfromer the core loss depends on volatage and cu
loss depnds on current so the both are voltage and current
(VA) so the tranformer rating is in Kva.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pradyumna chandra panda
Why the motors are rated in KW and transformers are rated in
KVA?
Ans . Motor is a consuming device it consume the power
(wt) so it is rated in KW. But the
Transformer is a static device which transfers
the power (Apparent power) from the
Generating point to the user. Apparent power is
the product of voltage and current
I.e. Increase voltage with decrease current and
decrease voltage with increase
current. Power factor of the load does not
affect apparent power it affect the Active
Power.
Active power is the real power which the transformer
gives. Transformer should not be rated on the base of
Active power (KW) which is variable because the power factor
of the load is not knows before which to be connected across
the transformer.
Reactive power Apparent power (k)
KVA
VI sin Q k
Kw
Q q
Active power VI cos Q
Active power is equal to apparent power at resistivity load
where power factor is unit at cos Q is equal to zero degree.
Active power is decrease power where cos Q (not fi) is
increase
Therefore in simple we can say due to unknown power factor
transformer and generator are rated in KVA.
Hint – we know cos FI is the value of cos Q i.e. apparent
power/ active power
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / s saranraj(sri durgadevi polyt
Both the losses of the transformer is independent of the
power factor (cos phi), which means a transformer would not
make any change in the power factor, since both the losses
viz copper loss(depends on current) and iron loss(depends
on voltage) are independent of power factor, that is why a
Transformers rating is not on kW, but on KVA
(or)
because,ironloss is depends in voltage and cu_loss is
depends in current.so the transformer ratings in kva
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / vignesh
Thumb Rule - all AC power sources - Generators,
Transformers, UPS etc. are rated in KVA and all loads are
rated in Watt or Kilowatt..
AND hence there is no need of power factor.
KVA=V X A (FRO SINGLE PHASE TRANSFORMER)
KVA = 1.732 X V XA (FOR THREE PHASE TRANSFORMER)
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / m. jamshed
As transformers are the power source and every power source
is deigned for specifid value of current and voltage.
The amount of current in A/C circuits is greatly affected
by p.f.as if we take two examples for the same kw with
different p.f we will get different amount of current that
is high current for low p.f and vice versa.
For the transformers we do not know about the load p.f,so
it will be rated in kva to determined the exact value of
current it can provide.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / manikanta..{munna} geethanjali
load is something which dissipates energy..!! in case of
transformer , ideally a transformer is power source
device...and but this acts as load practically bcoz of
losses in it...!!!
coming 2 d rating any load is alwayz rated in kw..!! here
in a transformer the losses are due 2 copper and iron which
depend on current and voltage respectively...there fore v
rate the transformer in v*i !!!! and they is no use of
including powerfactor.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / aryan
Since transformer is a static there will not be any
rotational losses it have only iron loss depend upon
voltage and copper loss depend upon current
for AC supply systems like generator, transformer rating is
done in KVA because of inductance present in AC . we don't
know load is resitive or inductive
it is independent there fore it is measured in kva
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / hitesh g. dobariya
kVA is the unit for apparent power. Apparent power consists of active and reactive power. Active power is the share of the apparent power which transmits energy from the source (generator) to the user. Reactive power is the share of the apparent power which represents a useless oscillation of energy from the source to the user and back again.
It occurs when on account of some inertia in the system there is a phase shift between voltage and current. This means that the current does not change polarity synchronous with the voltage. But the heat generated in a winding as well as the eddy current losses generated in a transformer core depend on the current only, regardless of whether it aligns with the voltage or not.
Therefore the heat is always proportional to the square of the current amplitude, irrespective of the phase angle (the shift between voltage and current). So a transformer has to be rated (and selected) by apparent power.
| Is This Answer Correct ? | 2 Yes | 0 No |
for 750 kw LT load what will be the ht kva
What is Gnat,Ant,Rabbit &Dog overhead conductor? Please explain.
-What should be minimum value of insulation resistance and maximum value of earth resistance at any electrical instillation and what is method of testing the same.
Any one can explain if there is any harm from humming noise heard from air circuit breaker : we have 415 switch board having two incomers from transformers 3.3KV/415V , when bus coupler closed, and open one ACB incomer to work in one of the transformers, the current started hunting around 50 Amps, and heard humming noise from the air circuit breaker, although the load current was only 1200 amps while the ACB capacity is 2500 Amps, and the transformer 1600 KVA. The same didn't happen when taken the other transformer offline. Why this humming noise and current fluctuation? is there any implication or danger, bearing in mind that we just returned everything back to normal and stopped the maintenance of the transformer. Shall we go ahead and ignore this noise?
What is VVVF Drive ?
What do you meant by slip power recovery?
WHAT IS THE FULL FORM OF ONAN ( TYPE OF COLLING IN TRANSFORMER)
1. Design a counter which counts 0, 4, 8, 2, 6, and repeats using: 1.a using JK flip flops 1.b using T flip flops 1.c using D flip flops
why rotor resistance starter is not suitable for squrielcage induction motor?why it is suitable for slipring induction motor?
explanation of mesh bus bars
will the introduction of capacitor bank parallel with the induction load reduce power consumption
4 Answers Nokia, WAPDA Water and Power Development Authority,
Which machine u will prefer to use at where flameble gases are comming out & why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)