Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Initially motor starts with star connection ,after few
timing changes to delta connection, why the motor should
run continously in star connection,it gives high torque &
low current?

Answers were Sorted based on User's Feedback



Initially motor starts with star connection ,after few timing changes to delta connection, why the..

Answer / madhu

basically in star connection line current is equal to phase
current,it gives high starting torque. after motor reaches
pick up speed we changed to delta.because in delta line
voltage is equal to phase voltage& line current is root 3
times the phase current.if we run in star in running time
the power losses are more due to current is high. thats why
we changed star to delta.

Is This Answer Correct ?    18 Yes 3 No

Initially motor starts with star connection ,after few timing changes to delta connection, why the..

Answer / marikkani.m

The purpose of starter is to start the motor and to limit
the starting current.we are starting the motor in y-
connetion during this impedence of two windings put across
the line voltage hence the starting current gettinh
redeuced
but the motor rated capacity (out put torque)can only be
obtained when itis changed to delta connection this time
the voltage is incresed bu 1.732 time to meet the torque
(torque is direct proportion to square of supply voltage .

Is This Answer Correct ?    7 Yes 1 No

Initially motor starts with star connection ,after few timing changes to delta connection, why the..

Answer / velusamy

There are two reasons

1.To get high starting torque, motor runs at star for
predetermined duration and then changed to delta.

2.If the motor runs continuously , the capacity of the
motor is reduced by root 3 times (Capacity of motor
rating/1.7324) and hence motor will fail if the OL setting
is not reduced to 1.7324times of motor full load current).

Is This Answer Correct ?    6 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

Will any motor burn if voltage provided is lesser than the rated voltage???? If yes, then how is speed control possible with voltage control

0 Answers  


What are the earth resistance Standards of 66kv sub stations according to indian norms.

2 Answers  


types of motor starter

5 Answers  


Why 15Amp. MCB is suitable to carry load of 1.5Ton Ac please Explain?

0 Answers  


How can calculate the earthing strip of Copper/GI for rating of 30kV,discharge current 10KA Lightning arrester.

0 Answers   Raychem RPG,


During a temperature rise test of a bus duct, it is fed with 415 volts at 2000 amperes. Why dont we get an electric shock if we touch the bus bars?

7 Answers   ABB, SDBL,


WHAT IS THE SETTING OF OVERLOAD RELAY AND UNDER VOLTAGE RELAY IN PERCENTAGE?

2 Answers  


what is the relation between the leading pf and supply voltage?

1 Answers  


what is surge suppressor?

5 Answers   Essar,


why neutral wire don't shock?

9 Answers  


We have 11kV/110V three phase indoor potential transformer in 66/11kV Sub-station, where the failure of PT is frequently happening and the rating of the PT is 0.2 class accuracy, with primary star and seconday (two cores) star connected. Some experts has suggested to not to connect the PT Primary neutral to the ground because when transformer neutal NCT connection is loose; the faulty current will flow through the PT primary neutral, resulting into failure of PT. My question is: Is it necessary to remove the primary neutral connection of the PT from ground? if not, what would be the reason for failure of PT. Please guide me.

2 Answers   KPTCL,


why can tv operate at low voltage??

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)