Initially motor starts with star connection ,after few
timing changes to delta connection, why the motor should
run continously in star connection,it gives high torque &
low current?
Answers were Sorted based on User's Feedback
Answer / madhu
basically in star connection line current is equal to phase
current,it gives high starting torque. after motor reaches
pick up speed we changed to delta.because in delta line
voltage is equal to phase voltage& line current is root 3
times the phase current.if we run in star in running time
the power losses are more due to current is high. thats why
we changed star to delta.
| Is This Answer Correct ? | 18 Yes | 3 No |
The purpose of starter is to start the motor and to limit
the starting current.we are starting the motor in y-
connetion during this impedence of two windings put across
the line voltage hence the starting current gettinh
redeuced
but the motor rated capacity (out put torque)can only be
obtained when itis changed to delta connection this time
the voltage is incresed bu 1.732 time to meet the torque
(torque is direct proportion to square of supply voltage .
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / velusamy
There are two reasons
1.To get high starting torque, motor runs at star for
predetermined duration and then changed to delta.
2.If the motor runs continuously , the capacity of the
motor is reduced by root 3 times (Capacity of motor
rating/1.7324) and hence motor will fail if the OL setting
is not reduced to 1.7324times of motor full load current).
| Is This Answer Correct ? | 6 Yes | 2 No |
what is difference b/w CFL and Ordinary lamps? which one is useful for power saving?
Is any generator is developed which is operated with out diesal or other expensive source?
Why do we generate 3 Phase AC Supply? It is possible to generate 4 Phase and 5 Phase explain it?
what is the calculation of power factor?
why 30kva ups buzzing(hamming) sound?
2 Answers Madhya Pradesh Electricity Board MPEB,
What is the difference between earth fault and restricted earth fault protection?
what is the meaning of 5% droop or 7% droop in AVR?
11kV capacitor bank of rating 2.4KVAR, is charged with protective relays of only over current & Earth fault &.......without Over Voltage, Under Voltage & Neutral Displacement Relay. Is it advisable??
how we start 40w tube light with 4 diodes,2capacitors,1 choke and without starter.(a product avilable in market which lights burnt tube lights also)
why we r used APFC Panel in industrial area.when P.F. low then wat will be the effect in our system?
10 Answers ABB, Georgio Rocks, Piramal Healthcare, Zenith Engineering Corporation,
what is ATS & RING MAIN UNIT in Distribution System?And its Function.
Why the earth to phase voltage is high 250 compare to other two phases
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)