Initially motor starts with star connection ,after few
timing changes to delta connection, why the motor should
run continously in star connection,it gives high torque &
low current?
Answers were Sorted based on User's Feedback
Answer / madhu
basically in star connection line current is equal to phase
current,it gives high starting torque. after motor reaches
pick up speed we changed to delta.because in delta line
voltage is equal to phase voltage& line current is root 3
times the phase current.if we run in star in running time
the power losses are more due to current is high. thats why
we changed star to delta.
| Is This Answer Correct ? | 18 Yes | 3 No |
The purpose of starter is to start the motor and to limit
the starting current.we are starting the motor in y-
connetion during this impedence of two windings put across
the line voltage hence the starting current gettinh
redeuced
but the motor rated capacity (out put torque)can only be
obtained when itis changed to delta connection this time
the voltage is incresed bu 1.732 time to meet the torque
(torque is direct proportion to square of supply voltage .
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / velusamy
There are two reasons
1.To get high starting torque, motor runs at star for
predetermined duration and then changed to delta.
2.If the motor runs continuously , the capacity of the
motor is reduced by root 3 times (Capacity of motor
rating/1.7324) and hence motor will fail if the OL setting
is not reduced to 1.7324times of motor full load current).
| Is This Answer Correct ? | 6 Yes | 2 No |
where used impendence relay?
what are the types of cooling systems used in motors?
difference between EMVT, PT & CVT ?
if vcb make contact but output notreach give the reason?
what is the different between RCCB & ELCB
Why substation battery room is coulered black?
transmisssion type
Distinguish between neutral earthing and equipment earthing?
The magnitude of sum of two sinusoidal av voltage is equal to 230 volt.the magnitude of each individual voltage is also equal to 230 volt.what must be the phase difference between voltages?
0 Answers PGVCL Paschim Gujarat Vij Company Limited,
Why in celling fan stator are rotatig while rotor are steday
A distribution transformer giving afrequency of 200HZ, where it is rated for 50HZ. when it will occure?
what are the different types of bus bar used at electrical work at shelter
3 Answers Aster Teleservices, Costco,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)