Answer / saranraj
Transformer Both the losses of the transformer is
independent of the
power factor (cos phi), which means a transformer would not
make any change in the power factor, since both the losses
viz copper loss(depends on current) and iron loss(depends
on voltage) are independent of power factor, that is why a
Transformers rating is not on kW, but on KVA
because,ironloss is depends in voltage and cu_loss is
depends in current.so the transformer ratings in kva
| Is This Answer Correct ? | 18 Yes | 5 No |
Answer / girish kumar samal, hindalco,h
actually rating of a equipment depends upon heat , which
depends upon loss. as in transformer both copper loss &iron
loss dont depend upon power factor . so transformer rating
is in kva.
| Is This Answer Correct ? | 14 Yes | 4 No |
Answer / guest
ironloss depends on voltage and cu_loss
depends current.so the transformer ratings is in kva
| Is This Answer Correct ? | 20 Yes | 12 No |
Answer / love007
iron loss depend upon vtg & cu loss depend upon current
it threrotical also
we don't know load is pure resitive or inductive
so Xmer rating in KVA
b'coz in res load KW=KVA, inductive KVA=KW/COSpi
| Is This Answer Correct ? | 16 Yes | 8 No |
Answer / mahamuni raja
copper losses of a transformer depends on CURRENT and irons
of a transformer depends on VOLTAGE not an phase angle
between voltage and current. that is why transformer rating
in KVA not an KW.
| Is This Answer Correct ? | 40 Yes | 33 No |
Answer / asfaq
Transformer has two types of losses and they are iron loss &
copper loss.Iron loss depend on voltage while copper loss
depend current,also power factor is independent of both
losses.so rating is in KVA.one more reason is that we dont
know which type of load is connected to transformer.
Power=Voltage*Current*Powerfactor
Power factor is different for different typrd of load
so rating is KVA as per my knowledge
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / vijay saharan
the cu losses rating in curent and iron losses rating in
voltage so the both losses are trnsformer and this is the
cause trasformer rating in kva.
| Is This Answer Correct ? | 10 Yes | 5 No |
Answer / suresh
kVA is the unit for apparent power. Apparent power consists
of reactive and active power. Active power is the share of
the apparent power which transmits energy from the source
(generator) to the user. Reactive power is the share of the
apparent power which represents a useless oscillation of
energy from the source to the user and back again. It
occurs when on account of some »inertia« in the system
there is a phase shift between voltage and current. This
means that the current does not change polarity synchronous
with the voltage. But the heat generated in a winding as
well as the eddy current losses generated in a transformer
core depend on the current only, regardless of whether it
aligns with the voltage or not. Therefore the heat is
always proportional to the square of the current amplitude,
irrespective of the phase angle (the shift between voltage
and current). So a transformer has to be rated (and
selected) by apparent power.
| Is This Answer Correct ? | 14 Yes | 10 No |
Answer / ravi r estake
Because losses of transformer is dependent on current &
voltage probably copper & core losses.
| Is This Answer Correct ? | 15 Yes | 11 No |
Answer / amr mobarak
so For Active Power the Equation will be
P (primary) = P (secondary ) + P cu Losses + P iron Losses
Which can't describe our transformer with certain value in
both primary & secondary
| Is This Answer Correct ? | 7 Yes | 4 No |
What is the Procedure for selecting a Cable, Breaker and Transformer for particular load.
I have experienced electrical maintenance HT ,but I completed be ECE ....can I apply c license or not ???? Pls help me friend s...
Why only sinusoidal ac voltages are generated?why not triangular or sawtooth?
Is itnecessary to use capacitor in an Fluorescent Tube Light Fixtures? Why? What if not capacitors are not included?
ro plant grundfos bm30type pump.we start the pump using siemens 3rw 4423-1bc44, 30kw soft starter. bur its failier frequently. so we planed to change the dol starter. sp please tell me any budy its possible or not翿შ†
In power generator sets, when they are coverted from 50hz to 60hz, the kva rating after conversion increases. For example, the manufacturer of a perkins 200kva @ 50Hz generator set has mentioned it to become 220kva after converstion to 60hz. What is the relation between the frequency & the KVA rating. Any formula please.
Fot testing new star-delta 132 kw motor in electrical worshop.we should check in star or delta connection as we do not have higher capacity cable in worshop?
what r the advantage of selecting micro controller type tripping of circuit breaker than relay type tripping?
how is the leakage current flow only through guard wire (when guard wire is connected in the circuit)????
what happen when power factor of 2 parallely operated transformer become equle?
what happens when back charging of transformer is done for longer period
Transmission lines usually use a.3 phase b.2 phase c. Single phase
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)