why transformer ratings in kva?
Answer Posted / s saranraj(sri durgadevi polyt
Both the losses of the transformer is independent of the
power factor (cos phi), which means a transformer would not
make any change in the power factor, since both the losses
viz copper loss(depends on current) and iron loss(depends
on voltage) are independent of power factor, that is why a
Transformers rating is not on kW, but on KVA
(or)
because,ironloss is depends in voltage and cu_loss is
depends in current.so the transformer ratings in kva
| Is This Answer Correct ? | 5 Yes | 3 No |
Post New Answer View All Answers
How can we design a HVAC Plant room which includes AHU,FCU,Chillers,Cooling towers, Pumps etc & how will they work? any Drawing if possible?
please send me latest & previous years question papers for IOCL Technical level questions
explain me the relation between torque, frequency,speed,voltage and current in the 3 phase induction motor?
what is the difference between the characteristics of two different phase bushing of any transformer
I am inpecting a 10kVA UPS what tests should i do and should i observe?
Explain the advantages and disadvantages of hydropower plant?
how can we design robots
why does the magnetic balance tests at transformer?
Is it possible to measure correct value of earth resistance & cable insulation ristance with out disconncting earth lead & both sides of cable ends? If not, any other method to measure ER & CIR with out disconneting from the system.
Can 33kva/415v transformer be run underground? If the answer is yes why and if the answer is no why?
what do w do when the output of generator is fluctuating?
What is the tests required for a 132 kV, 400 kV , 765 kV for a Circuit Breaker and Power Transformer before commissioning ?
which protection used in power plant?
In case of HV test on medium voltage cables, BS is asking for 4 U0 where as IEC is asking for 3.5 U0. Can any one advise me how this 3.5 times or 4 times U0 is derived?
I HAVE BEEN SELECTED FOR APGENCO A.E(ELECTRICAL) 2008.HOW MUCH WEIGHTAGE FOR INTERVIEW AND WRITTEN TEST.HOW I HAVE TO PREPARE. PLEASE GIVE INFORMATION IF U KNOW.WHAT ABT G.D THIS TIME.CALL RATIO 1:2