How the Oil Surge Relay works? How it protect the OLTC?
Answers were Sorted based on User's Feedback
Answer / n. manohara rao
THE OIL SURGE RELAY IS CONNECTED IN BETWEEN OLTC CHAMBER AND CONSERVATOR (SEPARATE FOR FOR OLTC) WITH BREATHER. A SEPAATION SHOULD BE ARRANGE SUCH THAT THE OIL IN OLTC CHAMBER AND TRANSFORMER CHAMBER SHOULD NOT BE MIXED TOGETHER. IN CASE ANY ON LOAD TAPCHANGER A PROBLEMS DEVELOPED DURING OPERATION A GAS IS DEVELOPED AND THAT GAS WILL ACTUTE THE OIL SURGE RELAY AND AND THE RELAY ACTIVATES OTHER CIRCUITS AND MAIN CIRCUIT HT WILL BE OPNED WITH ALARAM INDICATION AND FLAG INDICATION
| Is This Answer Correct ? | 59 Yes | 17 No |
Answer / satish raman pathak
It is a gas operated relay.It is placed between Main Tank & Conservator Tank,with an angle5-7 Degree.There are2 Mercury switches, one in the top & other in the bottom of Bucholz relay,filled with Transformer Oil. When small amount of vapour passes through the relay Top Float will operate, gives Bucholz alarm.In case of heavy internal fault, Large amount of Bubbles forms,operates the Bottom Float , Gives Bucholz Trip.In case of Bucholz Alarm/Trip Relay contact to checked first(IN Alarm/Trip Relay contact will change).then if there was any gas formation occured.Gas should be relaesed through the top Vent of relay( in that time hissing sound is observed in case of Gas present).Have to release all other top vent in Main Tank & Radiator Top.
In case of OLTC, there are saperare OLTC Surge Relay, same as Main tank Bucholz Relay.
After gas release if Trafo again tripped in Bucholz.Then there must be some hot spot/heavy internal fault in Trafo.other necessory testing to be carried out, like Ratio test,Magnetic Balance test,Vector group test,IR Test for further fault finding.
| Is This Answer Correct ? | 3 Yes | 10 No |
Answer / subrahmanyam
We have faced the issue of Oil surge relay during rain. The
raly operated due to which complete plant tripped. First
GCB openeed and First out is turbine so tripped on turbine.
| Is This Answer Correct ? | 9 Yes | 17 No |
PLZ EXPLIN ABOUT CLASS PS CLASS CT .WHY THEY R DESINED AND FOR WHAT PURPOSE?WHY OTHER CT CANT BE USED AS PS CLASS CT? EXPLAIN IN SIMPLE LAUNGAGE IF POSSIBLE PLZ GIVE CIRCIT DIAGRAM?EMAIL-RAJ_SINGH_0376@SIFY.COM
WHY IS wet surface used for grounding???
Define magnetic centre in a motor?
We have Diesel generator of 200KW. fuel consumption is always same,even connected light load or full load. Is it right?
IN MY SYSTEM THERE IS ONLY OVER CURRENT EARTH FAULT RELAY IS AVAILABLE. FOR THE UNBALANCE SENSING IS THERE ANY RELAY IS AVAILABLE? THE SAME CTs WHICH ARE USED FOR THE OVER CURRENT EARTH FAULT RELAY CAN USE FOR UNBALANCE ALSO?
what is the formula for calculating the phase clerance between two phases and phase to earth how to calculate the cable for a motor
What is the actual calculation for transformer short circuit test?.
which fault is severe and why?between lll fault and lllg fault which fault is severe and y?
How can we step up ac and dc ?
What is the ratio of true power to apparent power in an ac circuit?
what is IP55,IP65
What is the difference between alternator and generator?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)