How the Oil Surge Relay works? How it protect the OLTC?
Answers were Sorted based on User's Feedback
Answer / n. manohara rao
THE OIL SURGE RELAY IS CONNECTED IN BETWEEN OLTC CHAMBER AND CONSERVATOR (SEPARATE FOR FOR OLTC) WITH BREATHER. A SEPAATION SHOULD BE ARRANGE SUCH THAT THE OIL IN OLTC CHAMBER AND TRANSFORMER CHAMBER SHOULD NOT BE MIXED TOGETHER. IN CASE ANY ON LOAD TAPCHANGER A PROBLEMS DEVELOPED DURING OPERATION A GAS IS DEVELOPED AND THAT GAS WILL ACTUTE THE OIL SURGE RELAY AND AND THE RELAY ACTIVATES OTHER CIRCUITS AND MAIN CIRCUIT HT WILL BE OPNED WITH ALARAM INDICATION AND FLAG INDICATION
| Is This Answer Correct ? | 59 Yes | 17 No |
Answer / satish raman pathak
It is a gas operated relay.It is placed between Main Tank & Conservator Tank,with an angle5-7 Degree.There are2 Mercury switches, one in the top & other in the bottom of Bucholz relay,filled with Transformer Oil. When small amount of vapour passes through the relay Top Float will operate, gives Bucholz alarm.In case of heavy internal fault, Large amount of Bubbles forms,operates the Bottom Float , Gives Bucholz Trip.In case of Bucholz Alarm/Trip Relay contact to checked first(IN Alarm/Trip Relay contact will change).then if there was any gas formation occured.Gas should be relaesed through the top Vent of relay( in that time hissing sound is observed in case of Gas present).Have to release all other top vent in Main Tank & Radiator Top.
In case of OLTC, there are saperare OLTC Surge Relay, same as Main tank Bucholz Relay.
After gas release if Trafo again tripped in Bucholz.Then there must be some hot spot/heavy internal fault in Trafo.other necessory testing to be carried out, like Ratio test,Magnetic Balance test,Vector group test,IR Test for further fault finding.
| Is This Answer Correct ? | 3 Yes | 10 No |
Answer / subrahmanyam
We have faced the issue of Oil surge relay during rain. The
raly operated due to which complete plant tripped. First
GCB openeed and First out is turbine so tripped on turbine.
| Is This Answer Correct ? | 9 Yes | 17 No |
why transformer rating in KVA or MVA instead of KW n MW??
in conventional fan regulators how the current varies with speed?
how can maintaince the acb contactor moveing and fixing kit
Why corona leads to production of Ozone and glow of the color VOILET?
HOW TO CALCULATE THE HEAT AND LOAD OF LT-SUBSTATION WHICH CONTAINS 2*1MVA TRANSFORMERS,LT-SWITCH BOARD,MLDB,ACB,BUSBAR,ETC,......?
why an ac solenoid valve attract the plunger eventhough we interchanges the terminal?will the ploes changes?
what is the formula for calculating of dielectric strength of transformer oil.
What is differance between alternator and generator?
Why is the earth socket in an electrical plug outlet made thicker and lenghty?
Can the efficiency of transformer be measured with the help of wattmeter readings taken at primary and secondary side? Support the answer.
how dc generator produce voltage initially?
I have 480V Single phase and I am trying to figure how big of a transformer (KVA's) and Primary breaker size I need to provide 200 Amps at 240V for a building.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)