How the Oil Surge Relay works? How it protect the OLTC?
Answers were Sorted based on User's Feedback
Answer / n. manohara rao
THE OIL SURGE RELAY IS CONNECTED IN BETWEEN OLTC CHAMBER AND CONSERVATOR (SEPARATE FOR FOR OLTC) WITH BREATHER. A SEPAATION SHOULD BE ARRANGE SUCH THAT THE OIL IN OLTC CHAMBER AND TRANSFORMER CHAMBER SHOULD NOT BE MIXED TOGETHER. IN CASE ANY ON LOAD TAPCHANGER A PROBLEMS DEVELOPED DURING OPERATION A GAS IS DEVELOPED AND THAT GAS WILL ACTUTE THE OIL SURGE RELAY AND AND THE RELAY ACTIVATES OTHER CIRCUITS AND MAIN CIRCUIT HT WILL BE OPNED WITH ALARAM INDICATION AND FLAG INDICATION
Is This Answer Correct ? | 59 Yes | 17 No |
Answer / satish raman pathak
It is a gas operated relay.It is placed between Main Tank & Conservator Tank,with an angle5-7 Degree.There are2 Mercury switches, one in the top & other in the bottom of Bucholz relay,filled with Transformer Oil. When small amount of vapour passes through the relay Top Float will operate, gives Bucholz alarm.In case of heavy internal fault, Large amount of Bubbles forms,operates the Bottom Float , Gives Bucholz Trip.In case of Bucholz Alarm/Trip Relay contact to checked first(IN Alarm/Trip Relay contact will change).then if there was any gas formation occured.Gas should be relaesed through the top Vent of relay( in that time hissing sound is observed in case of Gas present).Have to release all other top vent in Main Tank & Radiator Top.
In case of OLTC, there are saperare OLTC Surge Relay, same as Main tank Bucholz Relay.
After gas release if Trafo again tripped in Bucholz.Then there must be some hot spot/heavy internal fault in Trafo.other necessory testing to be carried out, like Ratio test,Magnetic Balance test,Vector group test,IR Test for further fault finding.
Is This Answer Correct ? | 3 Yes | 10 No |
Answer / subrahmanyam
We have faced the issue of Oil surge relay during rain. The
raly operated due to which complete plant tripped. First
GCB openeed and First out is turbine so tripped on turbine.
Is This Answer Correct ? | 9 Yes | 17 No |
If a Power Transformer Fails and the transformer manufacturer suggest that "Do all electrical test on the transformer?". What are the test to be conducted in this condition?
In Ferantti Effect Receiving end voltage is greater than sending end voltage but how it is possible. I know its all about charging current but give me some more detailed explaination?
What is the difference between AVR and Servo Stabliser
how we can calculate power factor in single phase & three phase ?thank u
Which type of a.c motor is used in the fan (ceiling fan, exhaust fan, pedestal fan, bracket fan etc) which are find in the houses ?
Though transformer consist winding which usually cause reactive power change in both generator and motor but it wont affect reactive power passing through transformer why?
how to calculate the distance relay faulty zone?pls explain?
i asked a funny question in Electrical ohms law V=IR in const temp voltage is directly proportional to current Power p=VI cos@ in that formula Voltage is indirectly proportional to current Try to give me the fact what is happening in Electrical.. contact Thanigai_1984@yahoo.co.in
What loads the lagging and leading effects comes in a circuit?
If we have two nodes A and B and Vab is the potential difference between these nodes then which node is called reference node a.node A b.node B c. Ground node
what happens if earth of 33kv cable is not connected to earthing pits? please send this query's answer to ngrm.sudha249@gmail.com
How the Oil Surge Relay works? How it protect the OLTC?