How the Oil Surge Relay works? How it protect the OLTC?
Answers were Sorted based on User's Feedback
Answer / n. manohara rao
THE OIL SURGE RELAY IS CONNECTED IN BETWEEN OLTC CHAMBER AND CONSERVATOR (SEPARATE FOR FOR OLTC) WITH BREATHER. A SEPAATION SHOULD BE ARRANGE SUCH THAT THE OIL IN OLTC CHAMBER AND TRANSFORMER CHAMBER SHOULD NOT BE MIXED TOGETHER. IN CASE ANY ON LOAD TAPCHANGER A PROBLEMS DEVELOPED DURING OPERATION A GAS IS DEVELOPED AND THAT GAS WILL ACTUTE THE OIL SURGE RELAY AND AND THE RELAY ACTIVATES OTHER CIRCUITS AND MAIN CIRCUIT HT WILL BE OPNED WITH ALARAM INDICATION AND FLAG INDICATION
| Is This Answer Correct ? | 59 Yes | 17 No |
Answer / satish raman pathak
It is a gas operated relay.It is placed between Main Tank & Conservator Tank,with an angle5-7 Degree.There are2 Mercury switches, one in the top & other in the bottom of Bucholz relay,filled with Transformer Oil. When small amount of vapour passes through the relay Top Float will operate, gives Bucholz alarm.In case of heavy internal fault, Large amount of Bubbles forms,operates the Bottom Float , Gives Bucholz Trip.In case of Bucholz Alarm/Trip Relay contact to checked first(IN Alarm/Trip Relay contact will change).then if there was any gas formation occured.Gas should be relaesed through the top Vent of relay( in that time hissing sound is observed in case of Gas present).Have to release all other top vent in Main Tank & Radiator Top.
In case of OLTC, there are saperare OLTC Surge Relay, same as Main tank Bucholz Relay.
After gas release if Trafo again tripped in Bucholz.Then there must be some hot spot/heavy internal fault in Trafo.other necessory testing to be carried out, like Ratio test,Magnetic Balance test,Vector group test,IR Test for further fault finding.
| Is This Answer Correct ? | 3 Yes | 10 No |
Answer / subrahmanyam
We have faced the issue of Oil surge relay during rain. The
raly operated due to which complete plant tripped. First
GCB openeed and First out is turbine so tripped on turbine.
| Is This Answer Correct ? | 9 Yes | 17 No |
while doing the excitation current test on power transformer what is the value of voltage to be applied? Nomonal rated voltage or 10% of rated voltage? Is it necessary to apply on high voltage side?
what is the clearances between phease to phease & phease to earth in 400 kv transmission line?
list the advantages of RCCB over other circuit breakers?
do we use neutral grounding for resistive balanced load? if we use what happen?
can we connect PARALLEL 2 D.G set with different rating?? How ? What is the requirement for this connections?
What are the classification of Servo Motor?
What is the function of mid point voltage in battery bank
1 Answers Jindal Steel and Power,
What are the different protection systems used to protect the transformer internally and externally?
Does the total power means fundamental plus Harmonics?
wht is this amps in power consuption and how can we convert that into consuption hours ? i am a sales executive of a energy saving lamps .
how to calculate the power factor when instantaneous voltage and current has harmonics in it ?
why the making current is more than then the breaking current and if its true then its about a controling circuit or breaker power contact points
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)