After synchronizing the running generator with grid, the avr getting tripped and the generator breaker also oettong tripped, before tripping the avr the pf meter of generator is showing leading pf please kindly give a suggestion to rectify this problem.
Answers were Sorted based on User's Feedback
If AVR trips UCB has to trip either for LOE(loss of excitation ) or reverse power .Leading pf indicates gen voltage lower than grid voltage . Check the measuring PTs. Is is better to synchronize manually before resorting to Auto. Check the synchroscope also
Is This Answer Correct ? | 2 Yes | 0 No |
As told by somebody , the phase sequence in the AVR should be as that of gen
Is This Answer Correct ? | 0 Yes | 0 No |
how to calculate the current carrying capacity of a conductor. How it is related to diameter of cable or conductor
As the one point of eac phase winding is connected to each other in satr connction. Even if that at distribution side collesion of two diff phases result in to blast. Why?
how to calculate capacitor bank value to maintain unity power factor plz xplain with some suitable xample?
The unit of quantity of electricity is the:(a) volt(b) coulomb(c) ohm(d) joule
why and where we use early make & late break contacts in protection?
what is the difference between static and dynamic induced emf?
14 Answers College School Exams Tests, MRF, Suraj Constructions,
Why birds seating in HT line does not get shock? If person hangs in HT line (single hand or both hands) does he get shock?
Is it good to short Neutral and Ground in the PLC or DCS main Power supply. Pls give YES or NO with reasons...? Simarpreet
what is merz price protection
can anyone plz tell me in 3 phase induction motor, whare we use STAR CONNECTED MOTOR and whare we use DELTA CONNECTED MOTOR
Whether the vacuum contactor requires Short circuit protection?If No,why?
why do the core of transformer saturates???