Answer / vinod
NGR capacity should allow the mininmum earth fault current
so that system with minimum earth fault current can be
detected and isolated by earthfault relay.
ie NGR fuction is to reduce the earth fault to the minimum
level in the range of earth fault relay
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / raghavendran.r
As far I know the formula is Rngr = Vln/Ig.
where Ig is the current flowing through the Neutral Grounding resistor(let through fault current), which depends upon the type of system you haver chosen, i.e High impedance grounding or Low resistance earthing.
The let through ground fault current through the neutral is low for High resistance earthing and its High for low resistance earthing.
But the important condition is that the let through fault current should be greater than the system capacitive charging current to avoid transient over voltage.
Is This Answer Correct ? | 2 Yes | 1 No |
What is the use of choke in tube light?
WHAT IS OLTC OF TRANSFORMER? WHERE IS ITS USED EITHER ON PRIMARY OR SECONDARY SIDE OF TRANSFORMER?
What is the rating of circuit breaker needed for 300 KVA load in 33 KV supply line in a transformer of 33 KV / 415 Volt ?
anybody can give the voltage value for 1M ohm
What is the difference between earth fault protection of motor feeder with CBCT and Without CBCT ?
0 Answers Enmas, Michelin, Reliance,
why the energy meter disc rotates anticlockwise while reading
what is meant by tranformer impedance?
Explain the function and difference of Restricted earth fault, simple earth fault and sensitive earth fault with connection diagram.
1.why motor rating in kw instead of KVA? 2.why alternators rating in KVA instead of KW?. 3.why transformer rating in KVA instead of KW?.
Is there any reason that we get shock on touching phase wire because the earth is at neutral potential? Is there any reason that the earth is at neutral potential because the neutral is earthed in apower station
how much flux density of CRNO core
What is cut-off rate?