Answer / soumik
if it is open circuited the whole current in the primary becomes magnetising current and a dangerously high voltage will appear across the secondary which will cause insulation breakdown and even something worse.so it,s secondary always kept shorted.
| Is This Answer Correct ? | 31 Yes | 1 No |
Answer / sandesh
Basic transformer formula:-
Vp x Ip = Vs x Is
Now our Vp > is very less (5 to 10V)
Ip > 2000A
Is > 1A
hence, Vs = (Vp x Ip)/Is
If Ct Secondary open circuited then Is = 0
therfore Vs = ( 5 x 2000)/ 0
Vs = ∞ i.e Infinity.
Which will harmful to Human Being.
Therefor CT Secondary never short circuited.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / leo thomas
In CTs only a negligible part of the primary ampere turns
is used to magnetising the core .Remaining ampere turns is
counter balanced by secondary due to shorted.Once opening
CT in energised condition high voltages presents in
secondary causing faintal shock and the CT core will damage
| Is This Answer Correct ? | 5 Yes | 0 No |
if it is open circuited the whole current in the primary
becomes magnetising current and a dangerously high voltage
will appear across the secondary which will cause insulation
breakdown and even something worse.so it,s secondary always
kept shorted.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is the comparison between 30mA DP RCCB and 100mA DP RCCB and can replace it against 63A MCB
what is meant by reactive power ?
why electron not flow in open loop,how they know path is open ?
Can Anyone suggest the Standards (IEC or IS) for selecting copper current density?
difference between generator and alternator
To determine the Healthiness of Insulation we will be performing Dielectric tests i.e Insulation Resistance test, Partial Discharge test,Switching Impulse, Lightning impulse, Tan Delta test ...etc why we required to perform this many test, why cant we do only one test. for Transformer, CT's
What is IDMT relay how it works.
3 Answers Electrotherm, Sulzer,
how hazordious area is classified at an oil & gas plant and categorise suitable class of electric equipment in that area like induction motors, LCS, Lighting Fixtures Fluerescent/Flood lights Mercury& sodium lights, J.Bs, Power Cables etc
The neutarl to earth voltage in system is 7volts on Electricity power but it lowers to 1.3volts when load transfered to DG power.what may be the reason.
Is there any design in the world a 220 KV transformer without breather …??????
what is transient enclosure vltage , very fast transients, very fast transient over voltages
What is RMU, and what it's function?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)