IF 5000amp current on LT 440V. then how much it will draw
amp on HT 11KV side
Answers were Sorted based on User's Feedback
Answer / prabhat ranjan
since, power will always be the same so power at LT side should be equal to HT side...
5000*440= I*11000
so.. I= 200AMP at the HT side
| Is This Answer Correct ? | 26 Yes | 1 No |
Answer / pradyumna171
the voltage ratio of HT< is 25:1 (11kv/44ov) then current ratio is inversly ie 1:25 if LT current is 5000 amp then HT current is 5000/25=200 amp. we get same answer by apply any method of calculate the current.
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / santosh soni
power is transfer for receiving end are same so all power is
transfer another side
5000*440=I*11000
I=200amp
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / guest
use your KVA formula. The va of your load is
root3 X 440 V X 5000= 3810511VA
SO AT 11KV SIDE IS
3810511/1.732 / 11000 =200 AMPS
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / shamsuzzaman
HT side 22 Amp for 11Kv Line , LT side ( 11 Kv/415 Volts ) how mouch ampere of ?
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / bharath
LT5000*440*1.732=3810400KVA
HTAMP 3810400/ 11000 =346.4amp
| Is This Answer Correct ? | 10 Yes | 8 No |
Answer / m.koteswara reddy
200A
I2= V1xI1/V2
( 440x5000)/11000=200A
| Is This Answer Correct ? | 3 Yes | 1 No |
5000/25=200amp (Receprocal ratio of voltage i.e 11000/440=25)
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pradyumna171
the voltage of HT< is 25:1(11kv/44ov) then current is 1:25(inversely) in this case if LT is 5000amp then HT current is 5000/25=200amp. we get the same answes by apply any method to calculate the current.
| Is This Answer Correct ? | 0 Yes | 1 No |
Can we pass 11kv power in 1.1kV voltage grade cable.If not why?.
how did i get the competency certificate as electricle supervisor. iam completed my b.tech.but i dnt have any experince, this certificate is required for applyng ongc mangement trainees. what should i do sir please suggested me
Please clarify 1. Icw: rated short circuit working withstand capacity 2. Icu: Rated ultimate breaking capacity 3. Ics: Rated service short circut withstand capacity 4. other specification of ACB
HAI SENT HPCL APTITUDE QUESTION PAPER, MY EMAIL ID IS angus_eee04@rediffmail.com,angus_eee04@yahoo.com
What is GNR ? How much value of ground neutral resistance?
Why stand-by earth fault relay and restricted earth fault relays are connected between neutral and ground in transformer?
do you have some of interview Questions in power and genrator section in general whith answers
why field resistance is higher than armature resistance in dc machines? and why filed resistance is kept at min value at starting in same time of armature resistance at max value?
In n high voltage 11kv system What happened if 1 of CT cable (IDMT) loose.Will e/f or o/c trip.please explain detail
why ligthing is not available in switch yards?
what do u understand from filter factor of reactor?
Explain what is Zener diode?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)