IF 5000amp current on LT 440V. then how much it will draw
amp on HT 11KV side
Answers were Sorted based on User's Feedback
Answer / prabhat ranjan
since, power will always be the same so power at LT side should be equal to HT side...
5000*440= I*11000
so.. I= 200AMP at the HT side
Is This Answer Correct ? | 26 Yes | 1 No |
Answer / pradyumna171
the voltage ratio of HT< is 25:1 (11kv/44ov) then current ratio is inversly ie 1:25 if LT current is 5000 amp then HT current is 5000/25=200 amp. we get same answer by apply any method of calculate the current.
Is This Answer Correct ? | 10 Yes | 2 No |
Answer / santosh soni
power is transfer for receiving end are same so all power is
transfer another side
5000*440=I*11000
I=200amp
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / guest
use your KVA formula. The va of your load is
root3 X 440 V X 5000= 3810511VA
SO AT 11KV SIDE IS
3810511/1.732 / 11000 =200 AMPS
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / shamsuzzaman
HT side 22 Amp for 11Kv Line , LT side ( 11 Kv/415 Volts ) how mouch ampere of ?
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / bharath
LT5000*440*1.732=3810400KVA
HTAMP 3810400/ 11000 =346.4amp
Is This Answer Correct ? | 10 Yes | 8 No |
Answer / m.koteswara reddy
200A
I2= V1xI1/V2
( 440x5000)/11000=200A
Is This Answer Correct ? | 3 Yes | 1 No |
5000/25=200amp (Receprocal ratio of voltage i.e 11000/440=25)
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pradyumna171
the voltage of HT< is 25:1(11kv/44ov) then current is 1:25(inversely) in this case if LT is 5000amp then HT current is 5000/25=200amp. we get the same answes by apply any method to calculate the current.
Is This Answer Correct ? | 0 Yes | 1 No |
it is possible to measurement of tension of slipring induction motor(SRIM)carbon brushes, any maesuring instruments are available in the markets.
why in India it is maintained for exactly 50HZ frequency, why it is not that 49Hz,why it is so?
what will happen at secondary side of transformer if i increase voltage at primary side?while V1*I1=V2*I2 will secondary voltage or current increase?
why we use isolation transformer?
what does mean of RCT and STR in diffrential CT?
How is magnetic leakage reduced?
If single phase supply is 220v. then why three phase supply is 660?
Can you any explain about active,reactive and apparent power in power system with example.
what is the practical definition for voltage
what is the difference between neutral
what is the advantage of using 3 phase line rather than using 2 phase line?
How can we convert the motor to generator and also generator to motor