Answer / anil
there should be a relative motion to induce an emf i.e
either a rotating rotor field with dc or alternating supply
to the stationary core in case of transformer if we give
constant dc than there is a constant flux linking with the
secondary which will not produce any emf in secondary and
thus since there is no opposition to the primary emf and
the resistance of winding is very small this will lead to
high currents in primary and thus may lead to the burning
this is not in case of alternator since the rotor is
rotating
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / yogesh
every conductor produces magnetic field around it when you give ac or dc supply.but in ac supply the flux is alternating which produces self induced emf in winding which opposes supply vtg so currunt limits.but in dc supply there is no self induced emf.so when dc supply given to xmer no self induced emf produced to limit the current and in alternator or dc motor there also no induced emf produced but to limit the current the winding resistance made high ie above 100 ohms wheres xmer wdg resistance is in points range ie 0.1 ohm etc
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / antaratara ghosh
With reference to the ans#2, the impedance of the
transformer is mostly inductance whereas in sync m/c it is
resistive...so if we apply a dc voltage in trafo, there
will be no inductance and the total impedance becomes very
very small.. thus I=(E-V)/Z will be very high for
trafo...due to this high current trafo windings will burn
but not sync m/c....
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / k.prakashchandra
The windings in both the cases will not burn out if the
cooling is perfect.When it comes to motors or gen, it is
advisable to specify whether field or armature instead of
just rotor or stator.In case of large HT gen, the field is
the rotor.When Dc is applied and current is =V/DC
resistance.The same with the Tr.At the rated DC current, the
heating in tr will be less as there are no iron losses.
| Is This Answer Correct ? | 0 Yes | 10 No |
What is vcb?
Why synchorised generators are used for the production of electricity?
% voltage variation in distribution a)1% b)5% c)10% d)15%
I have a generator of 300kw.400V,50hz . what is means can i assume the load Red Phase with Neutral 300kw.Yellow phase with neutral 300kw and Blue with neutral also 300Kw. or - red with neutral 100kw same as yelloe and blue phase also giving 100kw with neutral respectively
what is the differences between microprocessor and general purpose computer
for flour light (garden light) how much deep need to put 222ov 0
Should power factor be low or high?
what is the minning of propotional, integral, derivative ?
why do we require two lines one phase and a neutral for an ac transmission..is neutral potential zero..?if yes y carry a neutral line from generating station itself...why dont we take it from ground
1.what is difference between line,neutral and earth 2.IF single phase voltage is 230v ac and what should be the voltage between line to neutral,neutral to earth and earth to line
what will happen if the prime mover on the field excitation of the on-coming generator fails?Explain.
0 Answers Ahsanullah University of Science and Technology,
At which time Synchronous generator act as a Synchronous Condenser?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)