if transformer winding burn on dc supply then
why not alternator rotor winding please post
answer on y.sakhare@rediffmail.com
Answers were Sorted based on User's Feedback
Answer / anil
there should be a relative motion to induce an emf i.e
either a rotating rotor field with dc or alternating supply
to the stationary core in case of transformer if we give
constant dc than there is a constant flux linking with the
secondary which will not produce any emf in secondary and
thus since there is no opposition to the primary emf and
the resistance of winding is very small this will lead to
high currents in primary and thus may lead to the burning
this is not in case of alternator since the rotor is
rotating
Is This Answer Correct ? | 12 Yes | 3 No |
Answer / yogesh
every conductor produces magnetic field around it when you give ac or dc supply.but in ac supply the flux is alternating which produces self induced emf in winding which opposes supply vtg so currunt limits.but in dc supply there is no self induced emf.so when dc supply given to xmer no self induced emf produced to limit the current and in alternator or dc motor there also no induced emf produced but to limit the current the winding resistance made high ie above 100 ohms wheres xmer wdg resistance is in points range ie 0.1 ohm etc
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / antaratara ghosh
With reference to the ans#2, the impedance of the
transformer is mostly inductance whereas in sync m/c it is
resistive...so if we apply a dc voltage in trafo, there
will be no inductance and the total impedance becomes very
very small.. thus I=(E-V)/Z will be very high for
trafo...due to this high current trafo windings will burn
but not sync m/c....
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / k.prakashchandra
The windings in both the cases will not burn out if the
cooling is perfect.When it comes to motors or gen, it is
advisable to specify whether field or armature instead of
just rotor or stator.In case of large HT gen, the field is
the rotor.When Dc is applied and current is =V/DC
resistance.The same with the Tr.At the rated DC current, the
heating in tr will be less as there are no iron losses.
Is This Answer Correct ? | 0 Yes | 10 No |
1.Difference between vcb and Acb and partes. 2.Difference between STS and ATS.
draw the full wave and half wave circuit of 3 phase system and inverter circuit used in ups
in an industrical wiring, why we are using lighting DB and Power DB separately?
why alternator is used instead of dc generator and induction generator
why the manufacturer provide M and C terminals ? why they will not internally short them ?
Hello, im taking an introduction to PLC..and i'm having a hard time on creating a program for 2 lamps blinking alternately with this button characteristics: 1.) One push button (starts upon pressing) 2.) Same push button (when pressed again, will pause the system) 3.) Same push button (when pressed again, will continue the paused system) 4.) Same push button (when pressed within 2 seconds, will shut off the system) Pls..i know this is just a simple problem for you guys..
what does the word synchronous mean in 'synchronous machine'
Why 60Hz frequency is used in America what are all the benifits?
when we r using 3.5 cable for a bldg. and put laod on each phase using the neutral and neutral is the return paht for the phase so the current of the neutral must be Ir+Ib+iY (return).But the size of the netural is .5 as comper to the phase.
send me the upsc conventional papers of 2006
1 Answers Juniper Networks, Siemens,
When the load on the system is zero and Capacitor bank is on condition, is capacitor bank takes any load?
For some transformers we are using solid neutral earthing while some others we are using resistance earthing why ?