Answer / lakshmi
Yna0d1 means star connected hv winding with neutral brought
out, auto transformer with 0 degrees displacement. lv
winding delta connected legging hv winding by 30 degrees.
Y = star connection
n = neutral brought out
a = auto transformer
0 = zero degrees
d = delta connection
1 = 30 degrees lag
Is This Answer Correct ? | 84 Yes | 8 No |
Answer / sujeet pandey
you all people must be knowing about the symbols like YN and
d1 but what about a0. The 'a' represents that is
auto-transformer and 0 represents that there is 0 phase
difference b/w H.V. and I.V.(intermediate voltage) winding
since both are star-star. d1 means the transformer has a
tertiary winding which is delta connected and this delta is
lagging the H.V. winding by 30 degree.
There is no symbol for Intermediate voltage becoz all EHV
transformers are star-star connected.
Is This Answer Correct ? | 28 Yes | 1 No |
Answer / amir
Y N = HV winding in STARā connected with NEUTRAL., a=auto transformer with IV winding, oy= open LV winding and STAR connected 1=angle of deviation 1°
Is This Answer Correct ? | 1 Yes | 0 No |
how techometer works and how it will be connected above the flywheel in dg system
Is it necessary to seperate the DG earth grid with Electricity Board earth grid for protecting the DG set. if yes why?
how would you come to know if a transformer is double wound or auto? note that there is no tag. you are given only a multimeter.
How to calculate the size of the conductor for particular load
What is purpose of APFC panel?
7 Answers Techno Electric and Engineering,
After completing iti in electrician, how can i get certificate of electrical supervisor? What ia requirements. For it?
which is dangerous AC or DC? If so why?
What are Line losses and how can be it minimized/controlled.?
How transformer neutralshould earthed ? Transformer neutral connected to earth mat in substations, right or wrong ?
If a line which is drawing approximatly 2100amps what should be earthing streep size(using galwanize streep)?
why transformer is rated in KVA ?
How to reverse the direction of a DC motor ? By reversing the Armature wires or by reversing the field wires