I HAVE A 1 MVA TRANSFORMER, I WANT TO KNOW THE FAULT LEVEL OF
THE SYSTEM ( WHAT IS FAULT LEVEL PLEASE EXPLAIN WITH EXAMPLE)
Answers were Sorted based on User's Feedback
FAULT LEVEL MEANS SHORT CIRCUIT CAPACITY OF TRANSFORMER.YOU
HAVE NOT MENTIONED THE VALUE OF TRANSFORMER RATIO & % OF
IMPEDENCE.ASSUMED VOLTAGE RATIO= 11KV/415 V & % OF
IMPEDENCE=6%.
RATED FULL LOAD AMP OUTPUT =1MVA/(415 X 1.732)=1391.25A
SO SHORT CIRCUIT CAPACITY OF TRANSFORMER= 1391.25/6%
=23187.44 A
IF ANY FAULT OCCURED THEN THE ABOVE TRANSFORMER WITHSTAND
THE SHORT CIRCUIT CURRENT OF 23187 A.
Is This Answer Correct ? | 33 Yes | 4 No |
1 MVA, 11/0.415kV Transformer
Full load current= 1000000/(1.732x415) = 1391.24A
% Z(Impedance)=5 (As per IS 2026 for transformer ratings of
0.631 MVA to 1.24 MVA)
Fault current= IFL/%Z =1391.24/0.05 =27.824 kA
Is This Answer Correct ? | 18 Yes | 3 No |
Answer / raj l. lahare
For correct Fault level the DATA given is not sufficient. You need to give the Voltage Ratio and the % impedance of the Transformer.
Is This Answer Correct ? | 1 Yes | 0 No |
what type of protection used below 132KV feeders
11 Answers APTransco, Telecommunications, wbsedcl,
what is exact meaning of CT core saturation or simply saturation of core.
what is the function of governor in dg set
1 Answers Igarashi, Medispray, Reddy Labs,
can you send me the placement papers of electrical engg. from companis like NTPC,DRDO,IOCL,HPCL,BPCL etc.?If,plz send as soon as possible.Thanks.
how do we calculate length of starting time and repeated starting of a direct online starter?
what will happen if a cw rotating altenator being synchronized to ccw rotating altenator
What is the 415V AC Soft starter? Explain with an example?
star delta starter contorl circuit... drawing..
what r the tests on the 3 phase transformers can any one explain how to test using megger on transformers thx
why causes the burnt of AC Electrical Motor ?
WHAT IS VCB SAFETY
How can we calculate ngr resistance for a generator and Transformer ? What type of transformer requires ngr ?