I HAVE A 1 MVA TRANSFORMER, I WANT TO KNOW THE FAULT LEVEL OF
THE SYSTEM ( WHAT IS FAULT LEVEL PLEASE EXPLAIN WITH EXAMPLE)
Answers were Sorted based on User's Feedback
FAULT LEVEL MEANS SHORT CIRCUIT CAPACITY OF TRANSFORMER.YOU
HAVE NOT MENTIONED THE VALUE OF TRANSFORMER RATIO & % OF
IMPEDENCE.ASSUMED VOLTAGE RATIO= 11KV/415 V & % OF
IMPEDENCE=6%.
RATED FULL LOAD AMP OUTPUT =1MVA/(415 X 1.732)=1391.25A
SO SHORT CIRCUIT CAPACITY OF TRANSFORMER= 1391.25/6%
=23187.44 A
IF ANY FAULT OCCURED THEN THE ABOVE TRANSFORMER WITHSTAND
THE SHORT CIRCUIT CURRENT OF 23187 A.
Is This Answer Correct ? | 33 Yes | 4 No |
1 MVA, 11/0.415kV Transformer
Full load current= 1000000/(1.732x415) = 1391.24A
% Z(Impedance)=5 (As per IS 2026 for transformer ratings of
0.631 MVA to 1.24 MVA)
Fault current= IFL/%Z =1391.24/0.05 =27.824 kA
Is This Answer Correct ? | 18 Yes | 3 No |
Answer / raj l. lahare
For correct Fault level the DATA given is not sufficient. You need to give the Voltage Ratio and the % impedance of the Transformer.
Is This Answer Correct ? | 1 Yes | 0 No |
Are we do it in single transformer with dual primary as 11 KV and 33 KV and constant output as 415 Volts?.
if there is a voltage difference between neutral and earth when we operate any instrument for fraction of time then where is problem?
upto how much low RPM we will run the commercial motor which is run through VFD without any problem occurs in motor.Motor rating Duty is S1 & RPM is 1400.
how does WTI work ?
what is the max. acceptable leakage current in 33kv bus bar
A 30KW motor running at 1450 rpm draws 56A, how would you determine if this is correct or not?
can SMPS work in DC supply ?
10 Answers HCL, IBM, Reliance,
how i chosse capacitor bank if my energy meter is 48 kvr? tell me capacitor bank chossen formula?
Give atleast 20 alternating current apparatus and devices.
i want to know is it possible to generate usefull power by coupling generator with motor & supply gives to motor by battery source then generator generates power. remove the battery source given to the motor & feed the supply from some of the generated power supply to the motor & motor runs continously. generator generate power contnously.is it possible ?
How many safety of Disel Generator
How DC earth leakage currents can be reduced ?