how to calculate optimum loading for transformer?
Answers were Sorted based on User's Feedback
Answer / sathish n p
Take an example let tr rating is 2500KVA, 11KV/415v
TO calculate maximum loading on primary side
2500 X 10^3=1.732 X 11 X 10^3 X I
I=131.01Amps
Similarly Secondary side
2500 X 10^3=1.732 X 415 X I
I=3478 Amps
| Is This Answer Correct ? | 33 Yes | 5 No |
Answer / debashis
For determining the optimum loading of a transformer we need
to determine the load for which my copper loss would be equal to my iron loss.
At this point the loss would be at its minimum level and hence
the efficiency would be maximum.
Remember Iron loss is independent of load and copper loss depends on the load.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / elminshawy
Sorry Vikadeny
But how it is optimum if I bought a 100MVA transformer and
I only loaded it to 50MVA or 70MVA ?
for optimum loading of transformers please refer to IEC
standard (60354 Loading guide for oil-immersed power
transformers )
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rajendran
I think question refers to the optimum loading at which the
efficiency of the transformer is more/maximum...
if it is like that then we can refer the loading curves
provided by the manufacturer of the transformer....
generally as a thumbrule the optimum loading point is
around 85 to 95 percent of the capacity..
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / vikadent
As a rule of thumb, the optimum loading is between 50% to 70
% and my reference is Electrical installation guide by
Schneider and this is the range where the losses are minimum
inside the transformer.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / khalid hussain shaikh
POWER=1.732*VOLTAGE*CURRENT*POWER FACTOR
HERE POWER=2500KVA
VOLTAGE=11 KV
POWER FACOR AS STANDARD=0.85
I=?
I=2500KVA/1.732*11KV*0.85
KV CANCELLED EACH DENOMINATOR AND NUMARATOR,
I=2500/1.732*11*0.85
I=154 AMP (11 KV SIDE)
I=2500 KVA/1.732*415 V*0.85
V CANCELLED EACH DENOMINATOR AND NUMARATOR
I=2500 K/610.963
I=4.091 KA
I=4091 AMP
| Is This Answer Correct ? | 10 Yes | 16 No |
In a 3 phase system a neutral exists so that any unbalanced currents can flow through it towards earth.... but a phase demands a particular current as per the load attached to it....then where does the extra current come from the goes in the neutral??....I mean in an unbalanced system a phase demands a current as per its load attached....then where does the unbalanced current come from??
how does this job compare with others you have aplied for?
how does ELR works? explain
what factors to needed while selecting a MCB and MCCB
How will you Physically differentiate A.C and D.C motor?
What is the relation between the Peripheral speed(N) , no.of poles(P) and diameter(D) of a cylindrical rotor alternator ?
one KVAR takes how much amps, and how to add power capacitors to electrical panels, for example if one of the MCC drawn 800amps means how much KVAR required
the grid connection required for a 50 MegaWatt fotovoltaic powerplant is higher or lower than 35kv (high or medium tension)?
What is a formula to decide the size of the cable of the star delta motor ( From Contactor to the motor 2 runs )
What is fault level?How it is calculated and how it is Expressed?
What happen if LV supply is fed to a HT motor?
19 Answers ITC Infotech, Jindal,
sir, Is their any measuring unit of knoking? please explian?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)