What is the calculating formula for HT and LT amps in a
transformer.
Answer Posted / raju kumar singh
Let suppose u have taken 1500 kva transformer of 11kv to 415 v u wanna be the current calculation for the both HT side and LT side. But u also think that u have connect load of the transformer 1000 kw. In this case both HT & LT SIDE power drawn is same. But this is three phase so we take formula
P equal to SQ ROOT 3 *V* I COS phai
Remember cos phai is necessary becuse of we know KVA :::: KW/ COS phai
U have connect 1000kw and its drawn full lo
ad then it wil be calculate in HT SIDE
1000*1000:::1.732*11000*0.8* I(u take power factor as0.8)
I::::65.6A
WHILE calculating in LT SIDE IT wil be
1000*1000::: 1.732*440*0.8* I
I:::1739.05A
because power drawn HT & LT SIDE depend on load connected to the transformer
Is This Answer Correct ? | 31 Yes | 9 No |
Post New Answer View All Answers
I need to connect a synchronous generator to the grid using automatic synchronization and two circuit breakers (one for synchronization, one for end connection to the grid), how to determinate the required diameter of the cables?
please I wont know how to calculate the vector group for power transformer ZNyn11 best regard.
What does the term “voltage regulation” means?
what are the usual topology of transformers at different substations in the power system and why that particular topology is choosen. what are the limitaions of that topology?
explain the process of commutation in a dc machine. Explain what are inter-poles and why they are required in a dc machine.
Can you tell me more about pu systems (per unit systems )calculation in large power systems? how to get the base for voltage and power in generator, transformator and transmission lines?
if there are six generators (3 gas CATT, one Jenbacher o1 MW each, and two nos Diesel 01 no 01 mw other 0.65mw EDGs ( say), 3 CAtt gas set have identical pole pitch,01mw EDG and Jenbacher gas Set have different pole pitch, how their power connection can be done to connect a common bus bar during installation. in short, how different pole pitched generators power connection can be done to connect a common busbar system through generators incomer ACBs.
How the frame size of a flange mounted AC induction motor is calculated?
What is Tachometer used to measure?
What are the types of class b amplifier?
WHAT CAUSED THRESHOLD VOLTAGE TO EXIST?
what is the effect of power factor of machines in starting current
how ceiling fan worked?
Mr. mohh sahid m not satisfied for ur answer to the que weather the size of transformer increases or decreases withchange in fr for more detail go to the answer given by me
Pl. give me checklist for installation & commissioning of machine tool.