Answer / sgthakur
Obviously ths is permissible.
1. carry on the PI test of each trans.It should not be less
than 2.00
2.Kva rating must be same
3 Percentage impdence must be same if diff .,parallaling
can be done but trans load shsring may be diff.
4 vector Gr.must be same
5If the Trans. HT source coming fr. diff. source, before
connecting them parallel phase ballancing and phase
seq.test must be done.
6.Other paralling condn. ie freq., voltage must be same as
usual.
7. On LT side trans. tape must be kept in same pos.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / manoj dubey
apart from above said pl. also check for your switchgear
rating for fault current as you parallel the system your
system fault current level will increase so your system
should be able to take care of it.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
It is permitted if you have individual self protected switch
gears for outgoing feeders
Is This Answer Correct ? | 0 Yes | 0 No |
What is the permissible value of earth resistance!
How many straight through joint is permissible in single core 33kv XLPE cable for a length of 985 mtr.
What are the different types of cable jointing methods for HT and LT power cable?
give me battery AH calculation in U P S
it is possible to measurement of tension of slipring induction motor(SRIM)carbon brushes, any maesuring instruments are available in the markets.
Brief function of stepper motor
which motors is used in mixies
what is the ms flat constant for calculating earth mat design calculation?
How to assume answer to electrical questions
why HT voltage rating in multiple of 11
what is onan, onaf, ofan, ofaf in transformer?
what is pure resistive circuit and pure inductive circuit