we are using three transformer 33000/430 vac for three
separet block.all three transformer have three LT panel
separetly. can be Interconnected all three panel through bus
coupler. this is permissable or not by state electricity board.
Answers were Sorted based on User's Feedback
Answer / sgthakur
Obviously ths is permissible.
1. carry on the PI test of each trans.It should not be less
than 2.00
2.Kva rating must be same
3 Percentage impdence must be same if diff .,parallaling
can be done but trans load shsring may be diff.
4 vector Gr.must be same
5If the Trans. HT source coming fr. diff. source, before
connecting them parallel phase ballancing and phase
seq.test must be done.
6.Other paralling condn. ie freq., voltage must be same as
usual.
7. On LT side trans. tape must be kept in same pos.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / manoj dubey
apart from above said pl. also check for your switchgear
rating for fault current as you parallel the system your
system fault current level will increase so your system
should be able to take care of it.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
It is permitted if you have individual self protected switch
gears for outgoing feeders
Is This Answer Correct ? | 0 Yes | 0 No |
What will happen if the generator turns in a wrong direction?
Can any body tell gulf interview question for experienced electrical engineer ?
WHAT IS A BASIC DIFFERENCE BETWEEN THYRISTOR,TRIAC AND A DIAC.AND WHAT R THERE APPLICATIONS?
what is power factor
Why, the starting current of 3 phase Induction Motor is 7 to 8 times its rated current?
what is skin effect and why is it absent in DC systems
Hello Can I use step up HV transformer 440/4160V as a step down? Thanks Evgeny
What are the factors which influence the choice of specific magnetic and electric loadings of a synchronous machine?
What is the Impedance, inductive reactance calculations
How we calculate the spacing between the conductors in 11,33KV lines?
should Dy11 and Dy1 group can be operated in parallel??????
I did oil BDV test of 1600 KVA trafo 20KV/400V as per IEC 156. Result is 1) 58 KV 2) 58 KV 3)40 KV 4) 50 KV 5) 58 KV 6) 18 KV. Avr is 47 KV. Can we say oil is still ok even in the 6th test BDV is 18 KV ?