we are using three transformer 33000/430 vac for three
separet block.all three transformer have three LT panel
separetly. can be Interconnected all three panel through bus
coupler. this is permissable or not by state electricity board.
Answers were Sorted based on User's Feedback
Answer / sgthakur
Obviously ths is permissible.
1. carry on the PI test of each trans.It should not be less
than 2.00
2.Kva rating must be same
3 Percentage impdence must be same if diff .,parallaling
can be done but trans load shsring may be diff.
4 vector Gr.must be same
5If the Trans. HT source coming fr. diff. source, before
connecting them parallel phase ballancing and phase
seq.test must be done.
6.Other paralling condn. ie freq., voltage must be same as
usual.
7. On LT side trans. tape must be kept in same pos.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / manoj dubey
apart from above said pl. also check for your switchgear
rating for fault current as you parallel the system your
system fault current level will increase so your system
should be able to take care of it.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
It is permitted if you have individual self protected switch
gears for outgoing feeders
| Is This Answer Correct ? | 0 Yes | 0 No |
mounting of bucholz relay engle on transformer
What is the current flow in 230v ac supply ? What is the current flow in 415v Ac supply ?
Explain types soft starters?
Interchange 7 and 6 ,÷and× 36×7+4-7×3
Can we use HRC fuse inplace of semi conductor fuse ? What are difference between them?
In LRS how much water PH value maintain for good operation of motor?
An 11kv system consisting of an underground cable to a sub station about 300 meters away was shut down for about 10 hrs. On energising, it tripped off on earth fault about 10---20 mins later 6 times but since than it is not tripping.its already 3 weeks now. The SPAJ was found to be fine. what could be the cause.No test had been done to determine the cause of the trippings till now because of demand.
Why we are use 11KV / 22KV / 33KV / 66KV / 110KV / 230KV / 440KV this type of ratio. why cant we use other voltage ratio like 54KV / 99KV et.,
8 Answers College School Exams Tests, Hino, ITC Infotech, Reliance, UPRVUNL,
how to check regenerative load in drived motor
0 Answers Hindustan Unilever Limited, NHPC,
what is the working principle of smoke detector in fire alarm system
What is the need of earthing transformer for delta side of a transformer. (Think of a line section between a star/delta transformer at a grid substation and delta/star transformer at a village. An earthing transformer is there at the delta side of the star/delta transformer at grid substation). As there are no ground reference there will not be fault current if a one phase is grounded. Further L-L phase will be sensed by the primary side of star/delta transformer as a L-G fault. So why an earthing transformer is required at delta side
What are the material used for resistor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)