what is onan, onaf, ofan, ofaf in transformer?
Answers were Sorted based on User's Feedback
Answer / mrinal
Onan – Oil Natural Air Natural
Onaf - Oil Natural Air Forced
Ofan - Oil Forced Air Natural
Ofaf - Oil Forced Air Forced
Is This Answer Correct ? | 251 Yes | 6 No |
Answer / mick
it is the cooling method of a transformer
o = oil
n = natural means natural cooled i.e. by a radiator
a = air
f = forced means forced cooled i.e. with a fan
so an ONAN is a naturally cooled oil by natural flow of air
OFAF is oil is force cooled (heat exchanger) and the air is
forced (fans)
Is This Answer Correct ? | 152 Yes | 9 No |
Answer / xyz
ONAN,ONAF, OFAN, OFAF all these are the types of cooling
arrangements required in a transformer to cool the windings
which get heated due to continues passing of current in
them.
Is This Answer Correct ? | 73 Yes | 7 No |
Answer / mehedi islam aneek
The first letter designates the internal cooling medium in
contact with the windings.
O= mineral oil or synthetic insulation fluid with a fire
point ≤ 300°C
K = insulating fluid with a fire point > 300°C
L = insulating liquid with no me3asurable fire point.
The second letter designates the circulation mechanism for
internal cooling medium
N = Natural convection flow through cooling equipment
and in windings
F = Forced circulation through cooling equipment and
natural convention flow in the windings (also called
"directed flow")
D = Forced circulation through cooling equipment,
directed from the cooling equipment into at least the main
windings
The third letter designates external cooling medium
A = Air
W = Water
The fourth letter designates the circulation mechanism for
the external cooling medium.
N = Natural convection
F = Forced circulation (Fans (air cooling) , pumps
(water cooling))
For example: ONAN designates an oil filled unit that has
natural convection flow in the tank and utilizes natural air
convection cooling externally.
If this transformer has fans added for forced air
externally, the designation would be ONAF.
A transformer that has natural convection cooling as a base
rating and an elevated rating when fans were added later,
would be designated as ONAN/ONAF.
High fire point fluids use the designation of "K" for fluid
type. Thus a naturally cooled high fire point fluid would be
KNAN and the same unit with fans would be KNAF.
Is This Answer Correct ? | 44 Yes | 3 No |
Answer / alan santos
IS A PART OF COOLING SYSTEM OF THE TRANSFORMER
Is This Answer Correct ? | 24 Yes | 21 No |
Answer / yims
The above answers are not far from the truth. However
ONAN is Oil-immersed natural cooling
ONAF is Oil-immersed forced-air cooling
OFAN is Oil-immersed forced-oil natural cooling
OFAF is Oil-immersed forced-oil forced-air cooling
......I trust this helps.
Is This Answer Correct ? | 8 Yes | 13 No |
Answer / set ramachandran- kcet-eee-266
onan onaf ofan ofaf are the parts of the transformer i
think.anyway please inform me the corect answer.............
Is This Answer Correct ? | 8 Yes | 82 No |
What is mean by voltage & current.
how we sesign the transformer give some specifion regarding design of transformers
how to claculate the ups load in KVA pls give the if any fourmoul?
what should be the acceptrd value of winding resistance for 2.5MVA transformer
1.25 kg of hydrogen are burnt with stiochiometric air, the mass of air in kg required is
How convergengr of nr method is not dependent on selection of slack bus and how gauss siedel method depends?
Does the isolator has a making capacity????????
FOR 16/20 MVA 132/33 KV ONAN/ONAF TYPE TRANSFORMER IT IS DESIGNED FOR 16 MVA WITH ONAN CONDITION.IT BECOMES 20 MVA UNDER ONAF CONDITION.LOAD LOSS IS GUARANTEED FOR 65KW AT 20 MVA AND % IMPEDANCE 13.75. PLEASE TELL US AT WHAT LOAD LOSS AND % IMPEDANCE IT SHOULD BE DESIGNED FOR 16 MVA AND WHAT WILL BE ITS EFFICIENCY AT 20 MVA?
What is your acheivements
how we can explain arc heatng?
What is the difference between Isolator annd Circuit Breaker.
21 Answers ABB, Lanco, NTPC, Power Grid, RInfra,
IF I USED VVVF DRIVE IN FAN APPLICATION MOTOR IN 6.6 KV ( 700 KW) MOTOR & DURING NORMAL RUN OPERATION TIME IF RPM SUDDENLY REDUCE IN MOTOR BY DRIVE(E. MOTOR RPM REDUCE SUDENLY 687 TO 550 RPM) WAHT WILL BE HAPPEND IN DRIVE