what is the charging battery current of 80 kva UPS/100AH
bocket make battery.
Answers were Sorted based on User's Feedback
Answer / abhishek
hey buddy u require 64 nos of battery. because it is a 384v
+- sytem.
and u reqiure a charging currrent of 10 amp.
the funda is 1/10 of battery capacity.
if any thing u require more pl mail me at
abhishekp_sawant@rediffmail.com
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / thowsif_emerson_csm team
For 100AH Rocket ES-12-100 Battery the Maximum Charging
Current is 25A..
Pls find the following link FYI,
http://www.way-india.com/rocket_battery_specs.html
How many number of Batteries do u hv for ur 80KVA UPS?????
| Is This Answer Correct ? | 0 Yes | 1 No |
difference between isolator and circuit breaker?????
How will you utilise electrical power? You can start from the generating station.
What is the difference between Earthing and Neutral?
Diagram on interconnectivity of 11kv transformer with RMU (i.e, one incoming and two outgoing or two incoming and one outgoing)
Draw a Block diagram of TWO UPS systems connected in Parallel in Paralled mode?
How much water ( Kilo Liters) a submercible pump of 35 HP can lift from Borewell of 6" and 900 feet dip.
what is feeder?
Design and explain a circuit to produce an unregulated full wave D.C supply.
A 100 kVA , 400 v/250 kv testing transformer has 8% leakage reactance and resistance on 100 KVA base . A cable has to be tested at 500 kv using the above transformer as a resonant transformer at 50 hz . if the charging current of the cable at 500 kv is 0.4 A find the series inductance required . Assume 2% resistance for the inductor to be used and the connecting leads . Neglect dielectric loss of hte cable . what will be the input voltage to the transformer ?
will the turbogenerator operate on leading power factor with out modification in the stator winding.
we all know that corona is nothing but ionization of air around the conductor and there by allowing current to pass through ionized air.but we are not getting any short circuit in between the respective phases though the air turned as a conductive media between them??
I have installed capacitor bank at secondary transformer. cos phi is increase. but on load (far from transormer), it still poor. Can anybody explain it??
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)