A 100 kVA , 400 v/250 kv testing transformer has 8% leakage
reactance and resistance on 100 KVA base . A cable has to be
tested at 500 kv using the above transformer as a resonant
transformer at 50 hz . if the charging current of the cable
at 500 kv is 0.4 A find the series inductance required .
Assume 2% resistance for the inductor to be used and the
connecting leads . Neglect dielectric loss of hte cable .
what will be the input voltage to the transformer ?
No Answer is Posted For this Question
Be the First to Post Answer
difference between slippring induction motor and Generator?
why transformer do not rotate?
How to calculate earth flat size for 250 Kva DG and transformer?
which is the best institute for PLC,SCADA,DCS in hyderabad
For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply was applied at the HV. Connection between Aa was made with a 2.5mm cable. As soon as power was switched on the cable caught fire and burnt. This test was then abandoned. It is noteworthy to say that a similar cable was also used in a similar transformer for the same. The cable did not burn and test was successfully completed with good result. What is wrong? Please, help me out.
how to protect motor in dol starter having capacity of 30 hp.40 hp?
what is meant by moulded case circuit breaker ?
Is itnecessary to use capacitor in an Fluorescent Tube Light Fixtures? Why? What if not capacitors are not included?
Iam deepthi.i completed my b.tech from electrical engineering.i want to prepare for civil services.i dont have much knowledge about these exams,but i have great zeal of cracking exams.plz provide me suggestions to which options i can select for optionals
why name plate detail HP/KW rating of a motor is different from measured value HP/KW using formula?
how we provide neutral earth on synchronising panel as per electrical standards?
in soft starter system for 375 KW 3 ph induction motor for multi stage vertical pump, two thyristers failed causing shorting of thyrister. the motor winding failed while starting.What is the cause and what is the effect in above case