difference between isolator and circuit breaker?????
Answers were Sorted based on User's Feedback
Answer / gtmanikandan
Isolator can be open in off load but Circuit Breaker can be
open or close in off or on loda
| Is This Answer Correct ? | 26 Yes | 3 No |
Answer / kunal
An isolator can be operted only at no load condition,because
there is no arc-quenching medium in isolator,where as
breaker can be operated at both On-load condition & off-load
condition,since it has arc-quenching medium.
| Is This Answer Correct ? | 22 Yes | 0 No |
Answer / suresh
You cant open a Isolator under load, while CB can be.
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / esam hamdy
An isolator is the gate of the voltage while a breaker is
the gate of the current in a bay. The isolator opens and
closes only on zero current while the breaker opens and
closes on zero current, full load current and short circuit
current so, the breaker has arc-quenching medium and the
isolator has not.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / trimurty prasad
Isolator can oparate in witout load.in ckt breaker we can
oprate with load and fault condition also.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / dharmesh
Circuit Breaker is a device which can
Make or break circuit under normal conditions either manually or through remote control.
and
Isolator or Isolating Switch is a device which is used to disconnect a part of the system for maintanance purpose and repairs.Isolator can open a circuit under no load condition only.If two isolators are connected on either sides of circuit breaker,then the circuit breaker must be opened before opening the isolators.
After perfoming maitanancee work on the circuit breaker,isolators must be closed first and then the circuit breaker must be closed to bring the system into operation.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sakkaravarthi soganur arakonam
isolator is on off-load devices,
circuit breaker is on - load device
| Is This Answer Correct ? | 2 Yes | 2 No |
-What should be minimum value of insulation resistance and maximum value of earth resistance at any electrical instillation and what is method of testing the same.
What is the safety protection? Name the protections of Transformer?
why m and c are shorted in wattmeter
Give me clear explanation.What is the Different Between Load break switch and Vacuum circuit breaker
On a 3 winding transformer YNynd11, how do you apply REF protection to the Delta tertiary winding that is supplying auxiliaries to a substation?
which type sylbuse involved
Dear sir, I completed DECE In the year 1995.Now i am working in a private company from last 10 years as an Electrical supervisor.The company having a 1000 KVA transformer.Now i try to apply "C" Licence. I am eligible or not.If not eligible,pls give solution.
hello!my name is sheikh iam preparing for indian engineering servieces,please send me the old question papers..to sheikhshaazforjobs@gmail.com
why the active power flow of some line is increased when the active power of out is cut ?
What is mathematical model of a control system?
how do we calculate cable sq mm size,that if 50 A load
how to do CT Burden test
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)