Answer / jinu
capacitor bank will improve the power factor towards the
supply side only. ie if you are measuring the power factor
before the capacitor bank it will show the improved power
factor. But the same time when you measure it after the
bank it will show you the load power factor not the
improved power factor.
Is This Answer Correct ? | 19 Yes | 0 No |
Answer / heamkumar
Capacitor Bank is used to improve the Power Factor.
As you said, Pf will increase only in the incomer side.
Because you have connected the capacitor bank in the
secondary side near the incomer. So if you need to improve
the pf near load, you need to place the capacitor bank near
the load, but according to the load. So if you put the
capapcitor banks near the load side, power factor will
improve not only in the load side, but also in the incomer
side.
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / joseph
Since the reactive power compensation (capacitor) is
provided on the LT side of the transformer, the
compensation will take place upstream from the point of
connection. Between the point of connection and the Load,
the reactive power still remains uncompensated. Hence, in
case the loads are not very small and vastly distributed in
the network, it is better to provide reactive compensation
at the load end itself. The only disadvantage is that
there should be arrangement to switch off these capacitors
when loads are not ON, otherwise, the capacitors themselves
would act as loads!
Is This Answer Correct ? | 3 Yes | 1 No |
first a fall caluclate the reactive power. after that
according to reactive power caluclate requied capacitor to
be arrange then u will increase power factor.
kVAr = KW {tan(cos^-1 Phi e) - tan(Cos^-1 Phi d)}
Where - Phi e = existing Power Factor.
Phi d = Desired Power Factor.
Is This Answer Correct ? | 2 Yes | 4 No |
Answer / niranajn
Because the capacitor abnk provides the ractive power
needed near a transformer but it cant provide the
kvar required by the line so the power factor is still
low
Is This Answer Correct ? | 1 Yes | 4 No |
what is bushing in transfermor
7 Answers Bokaro Steel, Visa Steel,
in a 740 kw dc seperately excited motor field voltage is constant about 17.4 volts and armature voltage is500 volts dc. how it is possible to have two different voltages from single transformer of output voltage 500 volts? if any difficulty in question contact ajitsingh.kadian@gmail.com
Importance of fault current in power transformers and how to monitor the same? How is it different from winding temperature?
What is the maximum breakdown voltage of 11KVA and 66 KVA power line and how it is calculated?
0 Answers Anglo Platinum, Narnarayan Electrical,
which model T or pie model is prefarable in power syatem
what is meant by leakage current of a capacitor?
Can any body tell gulf interview question for experienced electrical engineer ?
What core magnetic balance test of transformer? How to do this test in a three phase Star delta (star-LV, Delta-HV) transformer? How to measure and where to measure? thanks and regards Austin
22 Answers Neutech, Power Grid, TSSPDCL,
CAN U PLEASE TELL ME SOME G.D TOPICS FOR APGENCO INTERVIEW&G.D
Why r u using pf panel. what the uses
what will happen when ac is applied resistor,inductor,capcitor?
can anyone send me some sample question regarding power grid corp