in the pipe line if the control valve fails to respond to
controller action,by what means we can stop the flow in the
pipe line ?
Answers were Sorted based on User's Feedback
Answer / renjith
For every control valve there will be option to manually
close the valve by adjusting a screw.
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / priya sharma
u can stop the air supply with the control valve accessory
that is the AIR LOCK
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / nilmaheshin@yahoo.co.in....jit
Chitanya wrote correct answer. Priya and renjith are also
correct. But dear when any body is not present in field at
that time fail safe action is responding
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / karthikeyan
absolutely right answers(1&2)....we can operate in manually,and also to remove the air line because feed water control valve should be a air to open,in this if air fail it should be close....
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ashwin jain
but wat happen if no 1 is there to control
manually..chetanya's answer is correct....
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mrmk
Good Suggestion.But if a control valve fail to operate
there may be so many reason.In practical,If you want to
isolate/stop the flow immediately it can be done easily by
closing upstream isolation valve.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / deepak
if something stuck in control valve then what will u do??
| Is This Answer Correct ? | 1 Yes | 0 No |
An RTD is a_________________________.it works as follows
A temperature sensor (RTD) connected via a temperature transmitter is adjusted to give an output of 4ma at 60 deg and 20 ma at 600 deg. This output (4-20ma) from the transmitter is connected to an IGBT-inverter to control a high speed (-12,000 to +12,000 RPM) DC motor. And in the inverter it is programmed as, for 4ma the motor speed will be -3,000 RPM and for 20ma the motor speed will be +10,000 RPM. The question is : If the motor speed is +5,500 (RPM), what will be the temperature? (-sign indicates that the motion is in reverse direction).
How a oxygen sensor & analyzer work at boiler or furnace, whats the principle & science is beyond this,How O2 sensor sence & convert signal & move toward analyzer & analyzer show reading in percent?
HOW CREATED LP & HP PRESURES IN DRUM FOR DRUM LEVEL MEASUREMENT!
for oil & gas industries which zone is normally preferred? why? give its example?
Tell me the field calibration procedure step by step with diagram of temperature transmitter, temperature indicator, flow indicator, level indicator, control valve, thermocouple, pressure indicator (digital & analogue).
how to connect 3 wire 4-20 mA transmitter in Plc system PLC system and how explain how the measuring data communicate with plc system.
What is transmitter
what is electric motorised valve working principle.
draw shematic diagram of c/v positioner(smart type)?
what is all types of analyzer in water production plant?
How to convert gpm into inches of eater.I nerd formula with example so pls help me.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)