why we are using MARSHALLING PANEL? what is the role?
Answers were Sorted based on User's Feedback
Answer / maulik vyas
marshalling panels are used as interface between field
junction box & dcs control panel..
It also isolates the dcs panel from feild control panel..
Is This Answer Correct ? | 133 Yes | 9 No |
Marshalling means grouping of I/Os. Marshalling panel is
placed between the DCS system panel and field instruments.
In marshalling panel grouping of I/Os like Analog Input,
Analog Output, Digital Input, Digital Output and Pulse I/O
are done.From marshalling panel the I/O signals are
communicated to the system CPU/Controllers through
Isolation/Signal conditioners.
In marshalling panel we can easily identify the Input or
Output and easy diagnosis can be done in case of fault
finding.
Is This Answer Correct ? | 97 Yes | 6 No |
Answer / rajkumar
in addition to maulik points
3. marshalling cabinets location-- if located exactly will
save much cable cost and easy for maintenance people to
trace out cable routing and fault finding
Is This Answer Correct ? | 53 Yes | 10 No |
Answer / muhammad fawad azim
FUNCTIONS:
Signal conditioning, termination, signal isolation, cold
junction compensation, field device power supplies.
Is This Answer Correct ? | 15 Yes | 8 No |
Answer / rodney
There is a more practical reason for using a Marshalling Panel which becomes apparent if we imagine a multi-cable coming from the field and being connected directly to the I/O cards of a DCS. Whenever some kind of maintenance/test/check has to be performed just imagine the risk of interfering directly at an I/O card just to open some loop circuit. There would be the risk of touching another entry , loosing some bolt, and many other situations that could jeopardize the whole I/O card for some lack of other space specifically created to allow the proper access for maintenance and testing - the Marshalling Panel. Once the connections between all the I/O cards and a Marshalling Panel are done, tested and identified, no one wil have to deal with the I/O panel again, which means less risk and a proper place to do maintenance and testing, for there will be proper open/close connectors, fuses, isolators and all that the Project specifies.
Is This Answer Correct ? | 8 Yes | 1 No |
How to consider the flow directions for control valve (Globe) Is the there any easy understanding in order to select the flow directions?
what are the inputs (drawings) we need to prepare loop schematics??
What are the problems faced while testing HART instruments?
We Have Two Field bus Pressure Transmitters of Different Sensor Range (I.E One is of Lower range and Another is of Higher Range).Is same Process Line. My Question is Can i provide Saturation Limit to my field Bus Transmitter as We can provide Saturation current limit to HART Instruments. As During Low Pressure Both Working OK ,But During High Pressure, transmitter with Lower sensor range Goes to Fault mode as Beyond its Sensor Limit it can Measure, So may I provide Saturation point Some where to Suppress This Fault during High Pressure.
what is plc communication?
hi this is noor in my work spot, i arranged THERMOCOUPLE in the place of RTD. (in FEED WATER tank). can i use T/C or not?
What is the difference between modbus,fieldbus & profibus
what is function of PLC, and how is it work , explain with difination
1 Answers Bapco Bahrain Petroleum Company,
Q- Ordinary Water Tap is which kind of controller ? P , PI or PID i chose the option of ON - OFF type controller but ambiguity is that for different positioning of tap we get different flow
A length of steel pipe is used to carry sea water to a desalination plant. An adequate corrosion allowance must be specified and indicated in the piping specification, which affects the _________________________ of the pipe
Can any body help me,The GE Mark V control system is windows based or Dos based?
How do you calibration D.P transmitter? ?