Answer / maulik vyas
marshalling panels are used as interface between field
junction box & dcs control panel..
It also isolates the dcs panel from feild control panel..
Is This Answer Correct ? | 133 Yes | 9 No |
Marshalling means grouping of I/Os. Marshalling panel is
placed between the DCS system panel and field instruments.
In marshalling panel grouping of I/Os like Analog Input,
Analog Output, Digital Input, Digital Output and Pulse I/O
are done.From marshalling panel the I/O signals are
communicated to the system CPU/Controllers through
Isolation/Signal conditioners.
In marshalling panel we can easily identify the Input or
Output and easy diagnosis can be done in case of fault
finding.
Is This Answer Correct ? | 97 Yes | 6 No |
Answer / rajkumar
in addition to maulik points
3. marshalling cabinets location-- if located exactly will
save much cable cost and easy for maintenance people to
trace out cable routing and fault finding
Is This Answer Correct ? | 53 Yes | 10 No |
Answer / muhammad fawad azim
FUNCTIONS:
Signal conditioning, termination, signal isolation, cold
junction compensation, field device power supplies.
Is This Answer Correct ? | 15 Yes | 8 No |
Answer / rodney
There is a more practical reason for using a Marshalling Panel which becomes apparent if we imagine a multi-cable coming from the field and being connected directly to the I/O cards of a DCS. Whenever some kind of maintenance/test/check has to be performed just imagine the risk of interfering directly at an I/O card just to open some loop circuit. There would be the risk of touching another entry , loosing some bolt, and many other situations that could jeopardize the whole I/O card for some lack of other space specifically created to allow the proper access for maintenance and testing - the Marshalling Panel. Once the connections between all the I/O cards and a Marshalling Panel are done, tested and identified, no one wil have to deal with the I/O panel again, which means less risk and a proper place to do maintenance and testing, for there will be proper open/close connectors, fuses, isolators and all that the Project specifies.
Is This Answer Correct ? | 8 Yes | 1 No |
What is the basic difference between 2 Wire, 3 Wire and 4 Wire RTD
who discoverd ohms law?
can anyone can let me know in Eurotron Micro cal 2+ calibrator in milli amps source mode we are not able to get 20 milli amps output it only produces 1.52 milli amps out, but display shows increase in milli amps , and err6 displays, let me know how to remove the err 6.
send me model hpcl questions pleas..........my mail id mohideen.dharvesh@gmail.com
What are different types of valves?
Why is it necessary to use compensation leg to measure the liquid level in a closed or pressurized tank?
how to calibrate mass flow meter (Coriolis)? Example calibration range: 0 to 2500 kg/hr line size 3" fluid: Etheline glycol (MEG)
Sir, I am working as a Instrument Engineer in Grasim Industries. Can any body provide question answer for interview purpose
what are turbo generators?
What is the difference between EPROM & EEPROM.
i want to calibrate a transmitter in the range of -100 to 300 mmwc. How it is possible to measure -100 to 300?.
how to calculate interface capelary level transmetar lower S.G.0.54 and uper S.G. 0.26 and h=490 mm