Answer / s vedpathak
In closed vessals, the vessal pressure may vary.this can
cause erratic level feedback.But if DP LT is used it take
into account this vessal pressure as it acts on both LP &
HP side. So LT feedback is purely based on the head due to
vessal fluid.Wet leg & dry leg method can be used depending
on the application.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / vaishnavi
In the case of closed tank der will pressure acting above the liq also.So in this case inorder to get accurate measurement we need to measure both pressure so we use dpt.But in the case of an open tank there will atmospheric pressure above the liq surface.Hence we need not measure pressure above liq.moreover as radar involves reflection principle this cannot be used to measure both the pressures in the closed tank.
Is This Answer Correct ? | 4 Yes | 7 No |
A PLC is programmed to drive three motors A, B and C as follows : After running motor A for an hour, motor B should get ON and motor A should get OFF. And after running motor B for an hour, motor C should get ON and motor B should get OFF. And after running motor C for an hour, motor A should get ON and motor C should get OFF. (That is, a cyclic repetition with time period one hour) Now, the second condition is: If any motor gone faulty and is tripped, the consecutive motor should get ON and the faulty (tripped) motor should be eliminated from cyclic repetition. The remaining two motors should bear the cyclic repetition of one hour each. (For healthy motor take logic as high and for tripped motor take logic as low) Now, the third condition is: When motor A load(Amps) exceeds 60% of its rated load, motor B should get ON in parallel to motor A. And when both motors A & B are running in parallel, and if their load exceeds 60% of their rated load, motor C should also start in parallel to A & B. [Here the cyclic repetition is eliminated, until their loads become normal(40%)] [Take logic high(1) for load at 60% and logic low(0) for load at 40%] Now draw a flow chart or a ladder diagram to fulfill the above condition.
How to work DCS? how to get the signal from Field Instruemtns to PIB to Console?
How to calibrate RC Feeder system in thermal power station?,If any instrument available to calibrate it,ple inform me. make:stock,
If we increase only P what will be controller action ?
What does threshold mean? what does tolerance mean?
What is difference between reset and initialization in system.
What is the working principle of oxygen analyzers(zirconium oxide type) used in CFBC boilers?
3 Answers Bajaj, Kohinoor, Wartsila,
What is surge and how is it prevented, what is the purpose of bypass valve across AS valve.
Please explain the difference between instrument range and calibration range in terms of pressure transmitter? line design pressure: 93 bar operating pressure : 82 bar press Transmitter Range? calibration range ?
What is the main difference between the terms instrumentation and Automation?
why does mA signal preferred for signal transmission?