What is the right procedure for adjusting the gap voltage
of bently nevada vibration sensor?
Answers were Sorted based on User's Feedback
Answer / imran mansuri
for vibration sensor installation take digital multimeter
connect on proxymeter out signal + comma (-) now insert
first your proxyprobeon sahft untill it's not touch body
you will get 0 volt output now unscrew proxy untill you
get -9.0vdc or -10 vdc equal 50 mil this is procedure that
i know
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / rana mujahid
first check all the physical checks like,prob material is
correct for service,cable length is proper accroding to
proximeter,termination,supply is proper(-24vdc),etc..
after this connect volt meter with proximeter b/w out and com.
and try to adjust exact -10vdc but -9.5 to -10.5 are ok just
configured in systm.
| Is This Answer Correct ? | 7 Yes | 0 No |
give me the formula for analog to digital converter and also d to a converter
what is the characteristics of control valve?
how to rectify the poor signal strength in utrasonic digtial flow meter ,model:ge digital xce868i
Why MUX JB's are using only Temperature Element in Fundation field bus?
0 Answers Reliance Industries,
When we will do simulation for I/P?IF WE DO SIMULATION through which way either series or parallel?
what are the possible reasons if a control valve fails to open/close?
what is the procedure of O2 sensor(ABB) calibration?
What is modbus?
can u please give the exact ckt explaination of AC Drive related to industries.
how can be calibrate flow indication transmitter (rosemount) it shows excess milli amps nearly about 24 ma on full scale, but its scale was set on 20ma on full scale..???how can be simiulate..???
A temperature sensor (RTD) connected via a temperature transmitter is adjusted to give an output of 4ma at 60 deg and 20 ma at 600 deg. This output (4-20ma) from the transmitter is connected to an IGBT-inverter to control a high speed (-12,000 to +12,000 RPM) DC motor. And in the inverter it is programmed as, for 4ma the motor speed will be -3,000 RPM and for 20ma the motor speed will be +10,000 RPM. The question is : If the motor speed is +5,500 (RPM), what will be the temperature? (-sign indicates that the motion is in reverse direction).
can we connect instrument earth pit to electrical earth pit, if not why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)