Answer / maneesh
if the instrument is online calibration can be done by
closing the valve at downstream side.now the meter should
read zero if not recalibrate it.always remember while
calibrating magnetic flow mwter the meter should be filled
with fluid and fluid should be condectieve
| Is This Answer Correct ? | 21 Yes | 4 No |
Answer / r.ravikant
There is constant factor for every correspondence flow.
For example,in Krohne Marshall Magnetic flow transmitter
ther is 'GF' factor fix for correspondence flow,so use this
factor.
| Is This Answer Correct ? | 17 Yes | 8 No |
Answer / muzaffar ahmed
if the instrument is online calibration can be done by
closing the valve at upstream and downstream side.now the
meter should be
read zero if not recalibrate it.always remember while
calibrating magnetic flow meter the meter should be filled
with fluid and fluid should be conductive.
and other wise condition as such so you should be done by
analog to digital trim.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / muaz
i ewi
i want to know about supperssion and elevation
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / uc nayak
Magnetic flowmeter calibration method is only by taking known volume of flow through it by taking drop test method.Other than this you can simulate the flow convertor with specific simulator with spefic simulation factor only.
| Is This Answer Correct ? | 0 Yes | 1 No |
what is difference between call out and call log
Why Ma signal is using for control system?
whether radar level transmitter is applicable for the open tank
-/5A. What is the meaning and limitations of this in energy meter constant. It is a 3 phase LT Energy Meter. If this Energy Meter is connected through a CT of ratio 200/5 Amps, then what is the multiplying constant and how its will be calculated.
GWR radar transmitter working principle?
what is the process for double acting cylinder pneumatic for 32' v/v
how micro-processor and micro controller different from architecture
3 Answers Bhushan Power Steel,
can we connect instrument earth pit to electrical earth pit, if not why?
IS THEIR ANY AGEING EFFECT ON FLOW NOZZLE, ORIFICE, MANIFOLD, OR TRANSMITTER ?
What is duty of as-built engineer.
Explain the thermocouple and RTD?
why 4 to 20 ma? why cant some other range?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)