Answer / maneesh
if the instrument is online calibration can be done by
closing the valve at downstream side.now the meter should
read zero if not recalibrate it.always remember while
calibrating magnetic flow mwter the meter should be filled
with fluid and fluid should be condectieve
| Is This Answer Correct ? | 21 Yes | 4 No |
Answer / r.ravikant
There is constant factor for every correspondence flow.
For example,in Krohne Marshall Magnetic flow transmitter
ther is 'GF' factor fix for correspondence flow,so use this
factor.
| Is This Answer Correct ? | 17 Yes | 8 No |
Answer / muzaffar ahmed
if the instrument is online calibration can be done by
closing the valve at upstream and downstream side.now the
meter should be
read zero if not recalibrate it.always remember while
calibrating magnetic flow meter the meter should be filled
with fluid and fluid should be conductive.
and other wise condition as such so you should be done by
analog to digital trim.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / muaz
i ewi
i want to know about supperssion and elevation
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / uc nayak
Magnetic flowmeter calibration method is only by taking known volume of flow through it by taking drop test method.Other than this you can simulate the flow convertor with specific simulator with spefic simulation factor only.
| Is This Answer Correct ? | 0 Yes | 1 No |
What is MLFB number for Siemens?N How they are defined?Give me Answer with example like take any Signal module....
Please explain about FAT? What is the difference between FAT and SAT?
Describe the function of Accumulator into the Pump
what is diff b/w neutron and ground?
If a differential pressure transmitter is calibrated for 0~2500 mmH2o and transmits a 4~20mA dc signal. The transmitter is placed across an orifice plate which is sized to create 2500 mmH2o differential at 5000m3/Hr a) what is the flow rate when the transmitter signal is 13.0mA DC? b) what is the signal output of the transmitter when flow rate is 2500 m3/Hr ?
How to Calibrate Level Switch in field
wich is coming the first HAZOP OR SIL
please explain clearly in PID controller if We increase P only what will be action of the contrlere.
what is power factor?
Why we. Don't measure current in parallel? Why we measure current in series and why we measure voltage in parallel only?
2 Answers Almeer Technical Services,
What is an antisurge control system, how it works?
Boolean algebra
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)