We have AC-transformer 110/13.8kv,40MVA.If DC-Voltage=110kv
is applied in its primary what will happen?
Answers were Sorted based on User's Feedback
Answer / shivashankar
It will act as short circuit, bcoz the rate of change of
flux will induce voltage in sec,whereas in Dc there is no
such phenomenon ..R=V/I..if V=0 R=0/i ultimately R=0......It
nay tend the transformer to overheat ...
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / guest
Due to the high short circuit current (110KV/0 ohms) the
primary winding will burn..
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / vasudeva rao
according to the faraday emf is developed in the winding
when there is a rate of change of flux is present.
(E=dΦ/dt ) i.e time variant flux is present. but in d.c
current is constant i.e time invariant. here flux is
constant. so differentiation of constant is zero. i.e
dΦ/dt=0. i.e e=0.
it means winding gets serious short circuit.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mohammad saber
for any dc value the the transformer insulator will ichrist
because of the direct current ,and as we know the
transformer operation theory work on the the alternating
current generate the mutual between the transformer windings
| Is This Answer Correct ? | 6 Yes | 6 No |
Answer / prabhakar
since the primary winding is of thin guage with large no.
of turns as compared to its secondary winding i.e.,the
resistance of the primary winding will be more and so that
no more short circuit happens with the winding and
eventually no more secondary voltage appears at the
secondary.(as per the basic of transformer principle)
| Is This Answer Correct ? | 1 Yes | 2 No |
why should series motor be started with load and shunt motor should be started without load??????
why designer use kva rating instead of kw in transformer rating???????????????
which oil used in transformer?
why is the rating of transformer done in kva and not in kw.
What are insulation classes? Tell examples of each of them.
Why PS class CT is always preferred for Differential protection?
Corona occurs between two transmission wires when they (a) are closely-spaced (b) are widely-spaced (c) have high potential difference (d) carry d.c. power
in three 3.5 core aluminium ug cable. one cable is used for one phase by shrting R,Y and B wires and other 2 cables used for Y and b phases. balace 3 neutral wires are made common and connected to load. suddenly neutral current was more than line current what is the reason behind this?
what is the formula to calculate kva genset required for a given load in kw.
What is the formula for calculating impedance of transformers connected parallel at fault level 50KA?
can we synchronize star system generators with delta system transmission line ? and how ?
why u want to work in sail/ntpc as u r already in an it company where life is good, good environment no much tensions etc?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)