how we calculate the 30 KW 3phase electric motor current on
noload
Answers were Sorted based on User's Feedback
Answer / j.kesavan
30 KW MOTOR NOMALLY FULL LOAD 54 AMPS, BUT WITH OUT LOAD
30% CURRENT WILL TAKE,ANY THREE PHASE INDUCTION MOTOR WITH
OUT LOAD 30PERSENT CURRENT WILL TAKE.
| Is This Answer Correct ? | 258 Yes | 60 No |
Answer / d.g.skandan
No load current of a 3phase induction motor varies
according to its KW and rpm. Normally as a thumb rule
fraction HP motors (below 2.2KW) will be 50% of full load
current. Above 2.2KW may be 20% to 30% OF full load
current.
| Is This Answer Correct ? | 92 Yes | 23 No |
Answer / mahmoud
In=p/1.732*v*p.f
=30x1000/1.732*.8*380
=57A
Ino=57/3
19A
| Is This Answer Correct ? | 108 Yes | 46 No |
Answer / suresh
no standerd farmulla to calculate the noload current but as
a thumbrule 3 ph induction motor will draw 30% current on
no load but few motor will take 50 to 60 % current
| Is This Answer Correct ? | 65 Yes | 16 No |
Answer / suthan prabhu
Actually,there is no standard formula to calculate the
noload current of the motor.Normally 25% to 40% of full
load current of the motor.Also depending upon motor KW and
supplier..
| Is This Answer Correct ? | 54 Yes | 11 No |
Answer / vikram
P = 30 kw
V= 415
I = ?
PF =0.8
p= 1.732 VI PF
I = 30000/1.732*415*0.8
I= 52.17 Amp (Full load current)
No load current will be 30% of FL current
N.L Current = 30% * 52.17
NLC = 15.65 A (Without taking Efficiency of motor into account)
| Is This Answer Correct ? | 43 Yes | 2 No |
Answer / surajkant
practically the no load current of 3 phase motor varies
from 25% to 35% whereas in 1phase it is nera to full laod.
| Is This Answer Correct ? | 28 Yes | 15 No |
Answer / s.p.singh
There is no standerd formula for calculating no load
current, It depend on the desine and material used in
motor. There is a major role of material(winding wire&
stamoing)to anhancing the efficiancy of motor.
| Is This Answer Correct ? | 14 Yes | 3 No |
Answer / k.arivazhagan
3 ph induction motor will run 30% current on
no load but few motor will take 40% current
EXAMPLE:
KW=3.7KW,Amps=7.45,(Assume 40% Of No Load Amps)
No Load Amps = 7.45*0.4
= 2.98A
| Is This Answer Correct ? | 15 Yes | 6 No |
While connecting bulb in Series/Parallel,there is any difference in glowing
how to calculate ups and battery rating
i have 400/230v transformer and didnt done the neutral eatrhing. i connected one lamp to one phase and neutral to the earth. but the lamp is not glowing. again i connected neutral to earth and repeated the same. then the lamp is glowing. in the first condition i tested with a line tester also, at that time the tesrer is glowing what is happening i dont know can any one help me?
if we give connection of 100watts bulb through a single phase energy meter ,the disc of a meter rotates why it happens?
i need to calculate high voltage line power factor daily basics but there is meter reading kwh and kvah while calculating power factor kwh/kvah formula was right. for examble there is point c=13kwh c=1.8 lag c=1.2 lead and c=14.5kvah like that i know that p.f =kwh/kvah but c=1.8lag kvarh and c=1.2lead kvarh points i dont know if u know please reply
one hp 3phase motor what generate power factor
What is the formula for calculating impedance of transformers connected parallel at fault level 50KA?
what is the difference in using the 125% and the 250% factor of safety in calculating circuit breakers capacity for motors,which is more reliable to use the 125% or 250%??
How can we measure and monitor critical performance parameters of Diesel Generator Sets, both electrical and engine ?
what is phase to phase to phase to ground fault
What is the difference between Earth and Neutral?
what is resticted earth fault protection ? how did it protect & work in power transformer
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)