how we calculate the 30 KW 3phase electric motor current on
noload
Answers were Sorted based on User's Feedback
Answer / j.kesavan
30 KW MOTOR NOMALLY FULL LOAD 54 AMPS, BUT WITH OUT LOAD
30% CURRENT WILL TAKE,ANY THREE PHASE INDUCTION MOTOR WITH
OUT LOAD 30PERSENT CURRENT WILL TAKE.
Is This Answer Correct ? | 257 Yes | 60 No |
Answer / d.g.skandan
No load current of a 3phase induction motor varies
according to its KW and rpm. Normally as a thumb rule
fraction HP motors (below 2.2KW) will be 50% of full load
current. Above 2.2KW may be 20% to 30% OF full load
current.
Is This Answer Correct ? | 92 Yes | 23 No |
Answer / mahmoud
In=p/1.732*v*p.f
=30x1000/1.732*.8*380
=57A
Ino=57/3
19A
Is This Answer Correct ? | 108 Yes | 46 No |
Answer / suresh
no standerd farmulla to calculate the noload current but as
a thumbrule 3 ph induction motor will draw 30% current on
no load but few motor will take 50 to 60 % current
Is This Answer Correct ? | 65 Yes | 16 No |
Answer / suthan prabhu
Actually,there is no standard formula to calculate the
noload current of the motor.Normally 25% to 40% of full
load current of the motor.Also depending upon motor KW and
supplier..
Is This Answer Correct ? | 54 Yes | 11 No |
Answer / vikram
P = 30 kw
V= 415
I = ?
PF =0.8
p= 1.732 VI PF
I = 30000/1.732*415*0.8
I= 52.17 Amp (Full load current)
No load current will be 30% of FL current
N.L Current = 30% * 52.17
NLC = 15.65 A (Without taking Efficiency of motor into account)
Is This Answer Correct ? | 43 Yes | 2 No |
Answer / surajkant
practically the no load current of 3 phase motor varies
from 25% to 35% whereas in 1phase it is nera to full laod.
Is This Answer Correct ? | 28 Yes | 15 No |
Answer / s.p.singh
There is no standerd formula for calculating no load
current, It depend on the desine and material used in
motor. There is a major role of material(winding wire&
stamoing)to anhancing the efficiancy of motor.
Is This Answer Correct ? | 14 Yes | 3 No |
Answer / k.arivazhagan
3 ph induction motor will run 30% current on
no load but few motor will take 40% current
EXAMPLE:
KW=3.7KW,Amps=7.45,(Assume 40% Of No Load Amps)
No Load Amps = 7.45*0.4
= 2.98A
Is This Answer Correct ? | 15 Yes | 6 No |
I am having a DG set.The 415 V from Generator is step up to 460 v and then the same is used for Induction furnace. before Step up, I am connecting LT load to my factory use. When Induction furnace is in service from DG, when i try to start a motor, the generator is tripped.Please tell me the reason.
1.what is the reason for transformer and lightning arrester blast in 33kv system
Why synchronous motor is used in power factor improvement,dc series in lift
WHY L-G FAULT IS MORE SEVERE IN TERMS OF RRRV?
0 Answers Engineers India Limited,
Why the CT Secondary is rated as 5A generally?
difference between generator and alternator
wat is the criteria we use the diff. relay ?
want happens when a dc is given to a commutator
Dear sir please mera ye sawaal hai ki rccb ka kya kaam hota hai please answer hindi me dizyega dhanyya waad
What is the basic principle of operation of alternators/dc generators?
what purpose to use excaiter in DG.?
what is the relationship between phase & neutral