how we calculate the 30 KW 3phase electric motor current on
noload
Answers were Sorted based on User's Feedback
Answer / j.kesavan
30 KW MOTOR NOMALLY FULL LOAD 54 AMPS, BUT WITH OUT LOAD
30% CURRENT WILL TAKE,ANY THREE PHASE INDUCTION MOTOR WITH
OUT LOAD 30PERSENT CURRENT WILL TAKE.
| Is This Answer Correct ? | 258 Yes | 60 No |
Answer / d.g.skandan
No load current of a 3phase induction motor varies
according to its KW and rpm. Normally as a thumb rule
fraction HP motors (below 2.2KW) will be 50% of full load
current. Above 2.2KW may be 20% to 30% OF full load
current.
| Is This Answer Correct ? | 92 Yes | 23 No |
Answer / mahmoud
In=p/1.732*v*p.f
=30x1000/1.732*.8*380
=57A
Ino=57/3
19A
| Is This Answer Correct ? | 108 Yes | 46 No |
Answer / suresh
no standerd farmulla to calculate the noload current but as
a thumbrule 3 ph induction motor will draw 30% current on
no load but few motor will take 50 to 60 % current
| Is This Answer Correct ? | 65 Yes | 16 No |
Answer / suthan prabhu
Actually,there is no standard formula to calculate the
noload current of the motor.Normally 25% to 40% of full
load current of the motor.Also depending upon motor KW and
supplier..
| Is This Answer Correct ? | 54 Yes | 11 No |
Answer / vikram
P = 30 kw
V= 415
I = ?
PF =0.8
p= 1.732 VI PF
I = 30000/1.732*415*0.8
I= 52.17 Amp (Full load current)
No load current will be 30% of FL current
N.L Current = 30% * 52.17
NLC = 15.65 A (Without taking Efficiency of motor into account)
| Is This Answer Correct ? | 43 Yes | 2 No |
Answer / surajkant
practically the no load current of 3 phase motor varies
from 25% to 35% whereas in 1phase it is nera to full laod.
| Is This Answer Correct ? | 28 Yes | 15 No |
Answer / s.p.singh
There is no standerd formula for calculating no load
current, It depend on the desine and material used in
motor. There is a major role of material(winding wire&
stamoing)to anhancing the efficiancy of motor.
| Is This Answer Correct ? | 14 Yes | 3 No |
Answer / k.arivazhagan
3 ph induction motor will run 30% current on
no load but few motor will take 40% current
EXAMPLE:
KW=3.7KW,Amps=7.45,(Assume 40% Of No Load Amps)
No Load Amps = 7.45*0.4
= 2.98A
| Is This Answer Correct ? | 15 Yes | 6 No |
whether inrush current for lamps or capcitors should be considered cable sizing to feed that load.
why is the rating of transformer done in kva and not in kw.
advantages of vvvf drives over non vvvf drives for EOT cranes
Why we called L-G fault as line to ground fault why ground? suppose if a line falls on building roof then can we called these fault as line to roof fault? please explain why ground term is used here?
what is the right method of laying cable tray if we are using EOT crane in shed, better is below or up
a 100mva,400/200v transformer has leakage impdce of 10% draws a steady state line currentof---------------
What is short circuit analysis of electrical networks?What are the procedures to be followed for its calculation?
how i chosse capacitor bank if my energy meter is 48 kvr? tell me capacitor bank chossen formula?
What is the function of semicon in 33kv ht cable ?
can I connect 25KvA stepdown transformer(RYB-440V,UVW-240V) to the output of 15KvA,3-phase online UPS(440V phase to phase)please brief.
what is the contact resistance of vacume circuit breaker??
what is KSR type transmission tower? What is LSR type transmission tower?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)