Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how we calculate the 30 KW 3phase electric motor current on
noload

Answers were Sorted based on User's Feedback



how we calculate the 30 KW 3phase electric motor current on noload..

Answer / marcin

Equation with power factor in is the most correct. Several
issues shall be counted before estimating no load current :

- number of the poles

- power factor - there is a curve from the manufacturer
showing how this is changed in a function of power

- size of the machine

- speed

- way of feeding machine - DOL / inverter

Example :

500kW machine 690V 750rpm In=670A, No load - 285A (~42%)

500kW machine 690V 100rpm In=520A, No load - 180A (~34%)

Answer :

KW = 1.732 * V * I * cos phi * K

where K is a factor taking all other circumstances (0,7 to 1
where 1 is ideal situation) lower K for higher number of
poles, multispeed machines, specific construction etc...

Is This Answer Correct ?    6 Yes 4 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / r. n. sharma

Torque of a rotor depends on its diameter and weight along
with winding as well as material and methodology of
construction and also on applied bearings and lubrication. A
bulky, heavier rotor will draw more no load current than
small, light weight rotor. Formula : Torque (T) = qr (Where
q=Tangential force acting at PCD of winding due to effect of
current flowing through it, and r= distance of winding from
centre of the shaft). This torque only tries to rotate the
dead weight(W) of the rotor on no load. It can be said
T=qr=(W + rolling friction in bearings + wind resistance).
These all factors can be calculated easily and then finally
to arrive the result i.e. no load current, however bearing
frictional force and wind force can be ignored.

Is This Answer Correct ?    2 Yes 1 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / krishna

normally in KW p=vicos(phi)
if we have the value of (phi)...
then using power triangle method we can find kva and from that we can find our required answerthat is no load current

Is This Answer Correct ?    2 Yes 2 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / darshana sharma

At no load 30 kW, 3 phase electric motor will draw 30% to
40% of full load current.

Is This Answer Correct ?    2 Yes 2 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / vaibhav

There are many factors that decide no load amperes. Material characteristic of winding material, slip of motor, voltage applied, air gap between stator and rotor, motor bearing condition etc. Mostly rewinded motors show high no load ampere sometimes up to 70-80% of full load ampere. There is no thumb rule to calculate it and in case of new motor no load ampere value is generally mentioned on motor name plate.

Is This Answer Correct ?    1 Yes 1 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / janardan

For 2 pole motor; No load current will be the 1/3 of the Full load current.
i.e if motor takes 181.00 full load current then the no load current will
181 X 1/3 = 60.33 amp.

* for 4 pole: 1/3 to > 3/8
for 6 pole: 1/3 to <1/2
for 8 pole: 1/3 to 5/8

Is This Answer Correct ?    1 Yes 1 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / mathan.k

No load current of any induction motor is 21.5% of full
load current.

Is This Answer Correct ?    2 Yes 3 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / maheshwar das

12A

Is This Answer Correct ?    1 Yes 3 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / kailash vashisth

there is no such standard formulae but after a lot study i
found that for below 5 Hp motor Its 30% of full load
current and above 5 Hp its 45 to 50% of full load current

Is This Answer Correct ?    1 Yes 3 No

how we calculate the 30 KW 3phase electric motor current on noload..

Answer / watson

i think the no load current is

Root 3 times of Full load current
i.e

I nl = 1.732 X I fl

Is This Answer Correct ?    2 Yes 16 No

Post New Answer

More Electrical Engineering Interview Questions

In Round type three phase transformer why the LV side is inner part and HV outer part in the design of transformer? why they cant be opposite?

2 Answers  


How we can come to know the substation range,without go through any name plate ?

0 Answers   CG,


how circuit breaker work.. what is the operations taking place inside a circuit breaker when an overcurrent occurs... is it similar to fuse?

0 Answers   LTT,


one hp 3phase motor what generate power factor

1 Answers  


I want formula to calculate cable size as per load given in length & amp. I searched many sites but didn't right answer. Please reply me asap.

0 Answers  


The objective of connecting a resistance and capacitance across gate circuit is to protect the SCR against

2 Answers  


What's an AVR? What's its purpose in Generators?

4 Answers  


If any HVDC line is going with positive & negative(the negative usually have return path of current with earthing electrode). Now the question is if this HVDC earthed electrode which is using as return path and earthed any nearby 400kv or 220kv AC substation equipments. which will be the impact of this on AC substation & its equipment, how severe may be this and what should be the minimum distance require between HVDC earthed electrode and AC substation equipments? It's really an high engineering level question...Dare to answer and increase your knowledge.

0 Answers   MEIL,


Is there any particular formula for sizing the bus bar based on the current rating

1 Answers   Bunt Solar,


Why transformer is not rotating?

20 Answers   BARC, Nerolac,


Why hydropower is called renewable source of energy?

0 Answers  


Is there any calculation to find unknwon(unferroled) phases R Y B in alternator,3 phase motor anybody shoot my problem. how can we notice this is the respective phase?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)