how we calculate the 30 KW 3phase electric motor current on
noload
Answers were Sorted based on User's Feedback
Answer / marcin
Equation with power factor in is the most correct. Several
issues shall be counted before estimating no load current :
- number of the poles
- power factor - there is a curve from the manufacturer
showing how this is changed in a function of power
- size of the machine
- speed
- way of feeding machine - DOL / inverter
Example :
500kW machine 690V 750rpm In=670A, No load - 285A (~42%)
500kW machine 690V 100rpm In=520A, No load - 180A (~34%)
Answer :
KW = 1.732 * V * I * cos phi * K
where K is a factor taking all other circumstances (0,7 to 1
where 1 is ideal situation) lower K for higher number of
poles, multispeed machines, specific construction etc...
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / r. n. sharma
Torque of a rotor depends on its diameter and weight along
with winding as well as material and methodology of
construction and also on applied bearings and lubrication. A
bulky, heavier rotor will draw more no load current than
small, light weight rotor. Formula : Torque (T) = qr (Where
q=Tangential force acting at PCD of winding due to effect of
current flowing through it, and r= distance of winding from
centre of the shaft). This torque only tries to rotate the
dead weight(W) of the rotor on no load. It can be said
T=qr=(W + rolling friction in bearings + wind resistance).
These all factors can be calculated easily and then finally
to arrive the result i.e. no load current, however bearing
frictional force and wind force can be ignored.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / krishna
normally in KW p=vicos(phi)
if we have the value of (phi)...
then using power triangle method we can find kva and from that we can find our required answerthat is no load current
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / darshana sharma
At no load 30 kW, 3 phase electric motor will draw 30% to
40% of full load current.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / vaibhav
There are many factors that decide no load amperes. Material characteristic of winding material, slip of motor, voltage applied, air gap between stator and rotor, motor bearing condition etc. Mostly rewinded motors show high no load ampere sometimes up to 70-80% of full load ampere. There is no thumb rule to calculate it and in case of new motor no load ampere value is generally mentioned on motor name plate.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / janardan
For 2 pole motor; No load current will be the 1/3 of the Full load current.
i.e if motor takes 181.00 full load current then the no load current will
181 X 1/3 = 60.33 amp.
* for 4 pole: 1/3 to > 3/8
for 6 pole: 1/3 to <1/2
for 8 pole: 1/3 to 5/8
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / kailash vashisth
there is no such standard formulae but after a lot study i
found that for below 5 Hp motor Its 30% of full load
current and above 5 Hp its 45 to 50% of full load current
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / watson
i think the no load current is
Root 3 times of Full load current
i.e
I nl = 1.732 X I fl
| Is This Answer Correct ? | 2 Yes | 16 No |
what is the working principle of UPS?
Hi,Any one has idea regarding the KPTCL Recuirtments for AE'e & JE's for the year of 2009-10???Kindly help in regards..
in 11kv generators the neutral point is connected to earth via earth coil while in the 33 / 11 kv transformer the neutral point is connected to earth via earth resistor why?
can a generator with 15AH specified battery for starting can be connected to a battery of greater capacity?
What are the reason of unbalanced secondary voltage of HT transformer 33kv/6.6kv ? Incomming voltage is balanced.33kv each secondary voltage 6.6 kv 6.4 kv 6.4 kv At no load conditions.
when will cause the negative sequence falut in electrical system?
what is ATS & RING MAIN UNIT in Distribution System?And its Function.
what happen if one of 3-phase line has a much higher load when we are using delta to star transformer? how we can over-come from that?
what happen if rotor earth fault in AVR system?
How to PLC give the command to electrical
what will happen if earth of 33 kv cable (earthed system) is not connected to earthing pit?
What is the difference between PS & metering CT (5p20,0.5 etc.)? Why in PS class CT only Vk is given ? Is PS class CT is more accurate than metering CT?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)