Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why is the rating of transformer done in kva and not in kw.

Answers were Sorted based on User's Feedback



why is the rating of transformer done in kva and not in kw...

Answer / giridha

because the core losses and cu losses depends on only
voltage and current and is independent of power factor so
t/f rating is in KVA

Is This Answer Correct ?    50 Yes 8 No

why is the rating of transformer done in kva and not in kw...

Answer / manthesh.patil

transformer is rated in kva bcoz cu losses are dependent on
current and iron losses are dependent on voltage ,& they are
independent on powerfactor so transformer is rated in kva
not in kw

Is This Answer Correct ?    39 Yes 5 No

why is the rating of transformer done in kva and not in kw...

Answer / lakshmanan m

According to my opinion, manufacturer cant design the
particular transformer for specific load (capacitive or
inductive load) Thats why they dont give the power in KW.
Because KW= vxIx power factor. but power factor is
depending upon the load. So commonly they are give the KVA
power only. It means KVA= Vx I only. According to the load
we can calculate the KW rating.

Is This Answer Correct ?    18 Yes 0 No

why is the rating of transformer done in kva and not in kw...

Answer / manoj-essar

dear manoj, there is no concern of static or rotating
device, then why r u saying in this way?

Trafo is not having unity pf but it depends upon load type
of trafo...(inductive or capacitive or resistive load)

Is This Answer Correct ?    17 Yes 6 No

why is the rating of transformer done in kva and not in kw...

Answer / sachin /vaibhav

as core loss depends upon voltage & copper loss on
current independant of PF. HENCE RATING IS IN KVA

Is This Answer Correct ?    11 Yes 3 No

why is the rating of transformer done in kva and not in kw...

Answer / vasumalai madhavan

In transfomer, the core loss depends upon voltage and
copperloss depends on current , it was (transoformer) not
dependable on power factor . thats why the rating of the
transformer always in kva not in kw....

Is This Answer Correct ?    6 Yes 2 No

why is the rating of transformer done in kva and not in kw...

Answer / shinyvikram ganji

rating of the transformer is done based on losses(core and
copper losses).

Is This Answer Correct ?    4 Yes 2 No

why is the rating of transformer done in kva and not in kw...

Answer / ravi

transformer losses are in terms of current and voltage only
i.e (I Square R) copper loss and VI is the Core loss. i.e y
units are in KVA

Is This Answer Correct ?    3 Yes 1 No

why is the rating of transformer done in kva and not in kw...

Answer / beau

because transformer capacity takes care of both real power
consumed by resistive loads and reactive power in inductive
and capacitive loads such as motors and the transformer's
windings inductive reactance(Apparent power KVA).

Is This Answer Correct ?    4 Yes 2 No

why is the rating of transformer done in kva and not in kw...

Answer / thiyagarajan

kv is an apparent power kw is an active power the ratio
between active and apparent power is power factor ,we dont
know the power factor before connecting to load that why we
are used to refer kv in transmission

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

How can we convert the motor to generator and also generator to motor

2 Answers   Aesco,


If the circuit breaker will not close or it will trip, what will you do?

3 Answers  


why dc moter are not earthed ????

2 Answers  


what is the max working temperature of an oil filled transformer say of about 1500kva.

3 Answers  


How does ELCB work when exist earth foult? and How does RCCB work when exist earth foult?

1 Answers  


A cylindrical wire is compressed in length by 10%. The percentage decrease in the resistance will be?????

0 Answers  


what is tan delta point in a current transformer?

2 Answers  


What does the temperature (30 deg or 35 deg celcius) mark on conservator of transformer indicates?

2 Answers   MahaGenco,


WHY IS THE POWER FACTOR NOT MORE THAN UNITY.

6 Answers  


WHAT is the no of starts/hr for 3.3 KV, 300 KW motor. Motor is vertical flange type.

1 Answers   DAE, Siemens,


what is feeder bay?

0 Answers  


how moving coil indicator works?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)