How Much Capacity of Diesel Genset is suitable for
20 no.s of 1.5ton AC's & Why?(Load Calculation)
Answers were Sorted based on User's Feedback
Answer / vivek sri
Lokesh Thota & Girijapati Mishra are partly correct
1.5 Tons=5.25KW (1Ton=3.5kW)
Assuming COP of 2.5 Input KW = 5.25/2.5=2.1kW
If the AC is rated for 240 volts then
I=(2.1*1000)/(240*0.8)=10.94 Amps where 0.8 is the power factor.
For 20 Ac's I=10.94*20=218.75
In case you are using single phase generator with rated
voltage of 240 volts then the required genset capacity is
=240*218.75/1000=52.5kVA.
In case you are using a 3 phase generator with voltage
rating of 415 volts (L-L, Line to neutral voltage will be
240 Volts) then rating would
be=1.732*415*218.75=157kVA(1.732 is SQRT 3)
Is This Answer Correct ? | 1 Yes | 6 No |
What is ELCB?
difference between over current and over load protection?
why generator and t/f ratings given in kva?
What will be the capacity of the generator set which can be used for my 2 ton window air conditioner ?
what is the correct method for the outdoor termination of 19/33 KV HT cable step by step?
Why the Voltage rises when Leading Power Factor is occurs?
HOW TO DESIGN THE body EARTH cable(Copper Conductor) size for 60KVA UPS?
if i have one capacitor=80 micro farad which correct the unity power factor,but i want to make capacitor bank who correct the power factor.so,how to split this capacitance value?
what are the sections in a high voltage system(eg:incomer,buscoupler,isolator
What is the difference between Earthing and Neutral?
Insulater disk using formula for 33/66/135 line h t line
1 Answers Hofincons, Kirloskar, KPTCL,
WHAT HAPPEN IF TRANSFORMER HAS GIVEN SQUARE WAVE SUPPLY