How Much Capacity of Diesel Genset is suitable for
20 no.s of 1.5ton AC's & Why?(Load Calculation)
Answers were Sorted based on User's Feedback
Answer / vivek sri
Lokesh Thota & Girijapati Mishra are partly correct
1.5 Tons=5.25KW (1Ton=3.5kW)
Assuming COP of 2.5 Input KW = 5.25/2.5=2.1kW
If the AC is rated for 240 volts then
I=(2.1*1000)/(240*0.8)=10.94 Amps where 0.8 is the power factor.
For 20 Ac's I=10.94*20=218.75
In case you are using single phase generator with rated
voltage of 240 volts then the required genset capacity is
=240*218.75/1000=52.5kVA.
In case you are using a 3 phase generator with voltage
rating of 415 volts (L-L, Line to neutral voltage will be
240 Volts) then rating would
be=1.732*415*218.75=157kVA(1.732 is SQRT 3)
| Is This Answer Correct ? | 1 Yes | 6 No |
How to checked frequency drive output voltages?
what is reactive power ? what its role in transmission lines?
How many types are using in 220kv/400 kv swith yard
How can you calculate the size of the down conductor cable for the lightning protection system. Is 70mm2 cable can replace 95mm 2 bare copper cable when the copper tape size is 25Wx3 thk mm.
How to calculate Earth busbar size & what is the procedure we make for determine that?
Whether we used insulated line for 33KV supply. what we called it.
Can any body describe me why a soft starter is used for 6.6kv induction motor instead of VFD ?
Can any one help me how to set an overload set the range from 2.8A to 4A , rated motor current 22A, CT 60/5A
HOW TO CALCULATE THE APFC Panel Design
Energy metering: On the property I am renting, the supply voltage is 2 x 110 volts. These 2 x phases enter a energy meter which then exit the meter to over head lines to my house. Question 1. The meter is single phase 240 volts but is being used as 2 x phase(2 x 110volt), is this acceptable? if not, please give me the reasons. The meter details are as follows: 60Hz 15amp Imax 100 amp Kd 3,6 Wh/R 1 fase 3 hilos Model FX 231. I think it was manufactured in Brasil From this meter, the cables run along over head aluminum conductors,I estimate the cross sectional area to be 25mm diameter, but the neutral is only about 10mm square diameter, which cover a distance of 170 meters and then terminate with an underground cable of 65 meter length, total length = 235 meters. There must be a huge voltage drop over this length. This line is protected with 2 x 200 amp aluminum fuses after the meter, there is no main switch in the distribution board. These 2 phases connect directly onto 2 busbars. Surely the neutral should be the same size as the conductors if not more? Question2. What are your thoughts about this installation, should there be better protection, is the neutral too small? During the night, the lights dim then brighten all the time, this cannot be good for my electrical appliances. In my home, I only have a small electric geyser and fridge, my stove works off gas. But when i use other appliances like the washing machine or microwave oven, the light dim. The internal wiring of this house is done with solid hard drawn copper wires and of course, they have to be under rated. I am a retired electrician by trade, but not on the metering and over head mains side, my experience is on the factory maintenance side of things. Your expertise on these matters will be greatly appreciated. Please inform me how to rectify or make any improvements Kind regards, my power bill is very expensive, so I need to know how to bring it lower. Kind regards, Brian
why the emf of a cell more than the terminal voltage when the cell is delivering current?
what is the right method of laying cable tray if we are using EOT crane in shed, better is below or up
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)