How Much Capacity of Diesel Genset is suitable for
20 no.s of 1.5ton AC's & Why?(Load Calculation)
Answers were Sorted based on User's Feedback
Answer / vivek sri
Lokesh Thota & Girijapati Mishra are partly correct
1.5 Tons=5.25KW (1Ton=3.5kW)
Assuming COP of 2.5 Input KW = 5.25/2.5=2.1kW
If the AC is rated for 240 volts then
I=(2.1*1000)/(240*0.8)=10.94 Amps where 0.8 is the power factor.
For 20 Ac's I=10.94*20=218.75
In case you are using single phase generator with rated
voltage of 240 volts then the required genset capacity is
=240*218.75/1000=52.5kVA.
In case you are using a 3 phase generator with voltage
rating of 415 volts (L-L, Line to neutral voltage will be
240 Volts) then rating would
be=1.732*415*218.75=157kVA(1.732 is SQRT 3)
Is This Answer Correct ? | 1 Yes | 6 No |
Does the motor power displayed on the Motor name plate is the mechnical power motor delivers or it is consumed power from the system?
How to know the back up time for a 5KVA UPS which is connected to 15 nos. of computers? Is there any formula for this? pls. tell me.
What are the types of power in electrical power?
what is differnce between grounding and earthing or both are same?
What are the causes of motor vibration?
What you have to see in transformer after week, month?
what is the function of avr when synchronous generator act as synchronous motor
why induction motor speed is decress with increase in load? how synchronous motor speed is constant?
What happens if a +vely charged particle is placed in the centre of a room and assume that the north side wall is having magnetised with north polarity and south side wall is magnetised with south polarity. In which direction the particle will move
Why water bubbles when D.C. Current is passed through it? Why not when A.C. Current is passed?
WHAT HAPPEN IF LT SUPPLY 415 V FED TO THE HT 3.3KV MOTOR
how much insulation resistance 11kv & 33kv under ground cable between earth to phase & phase to phase.