Can any one help me how to set an overload set the range from 2.8A to
4A , rated motor current 22A, CT 60/5A

Answers were Sorted based on User's Feedback



Can any one help me how to set an overload set the range from 2.8A to 4A , rated motor current 22A..

Answer / k.prakashchandra

ct ratio is 12, hence full load current is measured as appx
2 amps by ct.You have to replace ct with 40/5 A or 30/5 A
ratio.

Is This Answer Correct ?    2 Yes 0 No

Can any one help me how to set an overload set the range from 2.8A to 4A , rated motor current 22A..

Answer / thirumoorthy s

the CT ratio is for metering only. so we cant set the O/L
setting for ur (2.8-4)A relay. u should provide correct O/L
relay. ie (18-25)A. the rated rating 22A, So we can set it
ion 20A.

Is This Answer Correct ?    3 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

What is basic difference between Soft Starters And VFD drives?

19 Answers   IBM,


i have ht transformer of 142 kva with air cooled facility,having secondary voltage 7850volt, and secondary connected full way bridge rectifier .i faced the problem repeatedly that transformer one coil and rectifier diode of two phase was burnt two times. i checked all the secondary ckt. no any short ckt found,then what will be the cause side

2 Answers   Modern Terry Towels,


why transmission lines traveled in high voltage?

5 Answers   TATA,


What is the Gap Should maintain for HT cables crossing of LT Cable?

2 Answers  


we often use the word HT (high tension) line.or we say HT switch gear, whats does HT basically mean. is it different from high voltage.

2 Answers  






in communication what is the role of elelctrical engineer?

3 Answers   Quippo, Reliance,


i need to calulate the cable size when watts are mentaind wat z the formula

1 Answers  


750kva 11/415kv transformer having percentage impedence is5.64%. 11KV HV whose current 39.37A and 415V LV whose current 1043.43A.resistance is 2.5ohm. find no load loss and full load loss?

2 Answers  


last week we did the REF relay test by closing single pole (R phase) of CB and apply 380V at the primary of delta transformer. we get 33A at the primary of the R phase star end. but we get 380A at both R an B in delta side. how and why?

1 Answers   Siemens,


with the help of drive can we run the 50hz motor on 100hz,what will be its effect.

3 Answers   BPL,


why generally transformer are in star to delta or delta to star used?

8 Answers   ABB,


How DC earth leakage currents can be reduced ?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)