what is different the DOL Starter and Star Delta STARTER
Answers were Sorted based on User's Feedback
Answer / natarajanramkumar
D.O.L Starter=Direct On Line Starter
1.It does not decrease the starting current.
2.It is cheap.
3.It connects directly the motor with supply for starting
as well as for running.
Star-Delta Starter
1.It decrease the starting current to 1/3 times.
2.It is costly.
3.It connects motor first in star at the time of starting
then in delta for running.
Is This Answer Correct ? | 257 Yes | 16 No |
DOL is Direct on line starter, it is used upto 50 H.P Motors
Star delta starter is Starting time Motor Phases are in Star
and Running time it is convert to Delta scheme.( Because
High H.P Motors are Starting time we are appling Low voltage
by using Star system, and it is increase the Torque.)
Is This Answer Correct ? | 161 Yes | 92 No |
Answer / ramanjaneyulu
DOL MEANS DIRECT ON LINE STARETER WE CAN USE DOL UP TO 5KW
RATEING IT CONNECTED DIRECT TO THE SUPPLY THROUGH OVER
LOAD RELAY IT DOES NOT REDUSE THE STARTING CURRENT. star
delta are used havy rateing motors because it limits the
starting current in 1/3 tmes of starting current
Is This Answer Correct ? | 50 Yes | 8 No |
Answer / sunil guru
DOL-- As its meaning suggests "DIRECT ON LINE" the motors are provided the direct supply without any changes & this starters are only used for protection purpose (not for soft starting of the motor)and are preffered only upto 10 Hp motors in industries....
STAR DELTA--- are preffered beyond DOL range
first reduced voltage(1/3 of supply V) is given to the motor & as it reaches 70-80% of its rated speed full V is given. (it is the function of changing 4m star to delta)is done to reduce the starting current and to protect the motor.......
for any disagreement mail me at parmar20072008@yahoo.com
Is This Answer Correct ? | 38 Yes | 8 No |
Answer / panil ahir
DOL is just running protection of motor while star-delta is running and starting protection of motor. It reduces the starting current of motor by increasing the resistance value of coils. As the starting resistance value is doubled the actual coil resistance, starting current reduces 1/3 times to protect the motor coils.
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / rohan k trivedi
DOL MEANS DIRECT ON LINE STARETER WE CAN USE DOL UP TO 110
KW MOTORS SPECIALLY WHERE THE STARTING TOURQUE IS LOW AND
STARTING KICK IS ALSO SMALL. WHILE STAR DELTA IS DESIGN TO
REDUSE THE HIGH STARTING KICK. GENERALLY FANS BLOWER AND
COMPERSSOR MOTORS HAVE HIGH STARTING CURRENT DURING THE
STARTING SO IT IS GOOD TO USE STAR DELTA INSTEAD OF DOL.
ANOTHER DIFFERENCE IS THAT DOL HAS ONLY ONE CONTACTOR WHILE
STARDELTA HAS THREE CONTACTOR.
Is This Answer Correct ? | 48 Yes | 40 No |
the dol is direct online ie if press the start button it
start direct by closing the single contactor.and star-delta
starter is by redusing the volatge this will helps to
incrase the traque.
Is This Answer Correct ? | 23 Yes | 20 No |
DOL Starter :
This starter is costwise cheap. it doesnot reduce the
starting current of the motor. The starting current of the
DOL starter is 6 to 7 times of the full load current. We can
use this starter for any higher kW range motors also even
6400kW motor.(In my working place using this DOL starter for
this 6400kW motor.
Note: for any standard cannot mentioned this much of the kW
motors only use in this type of starter nu..
Star/Delta Starter :
This starter is costwise higher. It can reduce the
starting current of the motor. The starter current of the
star/delta starter is 3 to 5 times of the full load current.
Generally in my working place this starter can be use above
75kW motors.
Is This Answer Correct ? | 23 Yes | 24 No |
What is the meaning of GRID?
Single line digram for 11 kV to distribution use go,la and do
what is raw power & normal power
why electron produce magnetic field when it is in motion?
which type of material is used to transformer laminated core?
Brief function of stepper motor
How much area a lightning arrestor can cover?
how to carry out Magnetizing Current Test on Distribution transformer and what purpose we are doing this test. why transformer rating in always in KVA ? what ispositive, negative, zero sequence impedence? How ElCB tripping if Neutral touch with ground Why AC & DC capacitor are use in UPS ? why motor rating in KW? how to syncronize two dg sets
Why we use CT on differant phases of 2ph.PT detection for brush-less static excitation of 3ph.,400v Synchronous Generator? What happen if use CT on same one of VT phase?
What is Procedure the procedure to select CT's & PT's in 66kV and above substation?
VCB in closed position during opertion if vaccume break then what will happend? it has any protection ?
send me the upsc conventional papers of 2006
1 Answers Juniper Networks, Siemens,