Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


what is different the DOL Starter and Star Delta STARTER

Answers were Sorted based on User's Feedback



what is different the DOL Starter and Star Delta STARTER..

Answer / natarajanramkumar

D.O.L Starter=Direct On Line Starter
1.It does not decrease the starting current.
2.It is cheap.
3.It connects directly the motor with supply for starting
as well as for running.
Star-Delta Starter
1.It decrease the starting current to 1/3 times.
2.It is costly.
3.It connects motor first in star at the time of starting
then in delta for running.

Is This Answer Correct ?    257 Yes 16 No

what is different the DOL Starter and Star Delta STARTER..

Answer / shankar rao

DOL is Direct on line starter, it is used upto 50 H.P Motors
Star delta starter is Starting time Motor Phases are in Star
and Running time it is convert to Delta scheme.( Because
High H.P Motors are Starting time we are appling Low voltage
by using Star system, and it is increase the Torque.)

Is This Answer Correct ?    161 Yes 92 No

what is different the DOL Starter and Star Delta STARTER..

Answer / ramanjaneyulu

DOL MEANS DIRECT ON LINE STARETER WE CAN USE DOL UP TO 5KW
RATEING IT CONNECTED DIRECT TO THE SUPPLY THROUGH OVER
LOAD RELAY IT DOES NOT REDUSE THE STARTING CURRENT. star
delta are used havy rateing motors because it limits the
starting current in 1/3 tmes of starting current

Is This Answer Correct ?    50 Yes 8 No

what is different the DOL Starter and Star Delta STARTER..

Answer / shafiq

in star/delta we can limit the current .but during starting
of motor in DOL motor will draw 3-5 time of its FLA

Is This Answer Correct ?    79 Yes 42 No

what is different the DOL Starter and Star Delta STARTER..

Answer / sunil guru

DOL-- As its meaning suggests "DIRECT ON LINE" the motors are provided the direct supply without any changes & this starters are only used for protection purpose (not for soft starting of the motor)and are preffered only upto 10 Hp motors in industries....

STAR DELTA--- are preffered beyond DOL range
first reduced voltage(1/3 of supply V) is given to the motor & as it reaches 70-80% of its rated speed full V is given. (it is the function of changing 4m star to delta)is done to reduce the starting current and to protect the motor.......

for any disagreement mail me at parmar20072008@yahoo.com

Is This Answer Correct ?    38 Yes 8 No

what is different the DOL Starter and Star Delta STARTER..

Answer / panil ahir

DOL is just running protection of motor while star-delta is running and starting protection of motor. It reduces the starting current of motor by increasing the resistance value of coils. As the starting resistance value is doubled the actual coil resistance, starting current reduces 1/3 times to protect the motor coils. 

Is This Answer Correct ?    10 Yes 1 No

what is different the DOL Starter and Star Delta STARTER..

Answer / rohan k trivedi

DOL MEANS DIRECT ON LINE STARETER WE CAN USE DOL UP TO 110
KW MOTORS SPECIALLY WHERE THE STARTING TOURQUE IS LOW AND
STARTING KICK IS ALSO SMALL. WHILE STAR DELTA IS DESIGN TO
REDUSE THE HIGH STARTING KICK. GENERALLY FANS BLOWER AND
COMPERSSOR MOTORS HAVE HIGH STARTING CURRENT DURING THE
STARTING SO IT IS GOOD TO USE STAR DELTA INSTEAD OF DOL.
ANOTHER DIFFERENCE IS THAT DOL HAS ONLY ONE CONTACTOR WHILE
STARDELTA HAS THREE CONTACTOR.

Is This Answer Correct ?    48 Yes 40 No

what is different the DOL Starter and Star Delta STARTER..

Answer / mallikarjun

the dol is direct online ie if press the start button it
start direct by closing the single contactor.and star-delta
starter is by redusing the volatge this will helps to
incrase the traque.

Is This Answer Correct ?    23 Yes 20 No

what is different the DOL Starter and Star Delta STARTER..

Answer / j.karthik

DOL Starter :
This starter is costwise cheap. it doesnot reduce the
starting current of the motor. The starting current of the
DOL starter is 6 to 7 times of the full load current. We can
use this starter for any higher kW range motors also even
6400kW motor.(In my working place using this DOL starter for
this 6400kW motor.

Note: for any standard cannot mentioned this much of the kW
motors only use in this type of starter nu..

Star/Delta Starter :
This starter is costwise higher. It can reduce the
starting current of the motor. The starter current of the
star/delta starter is 3 to 5 times of the full load current.
Generally in my working place this starter can be use above
75kW motors.

Is This Answer Correct ?    23 Yes 24 No

what is different the DOL Starter and Star Delta STARTER..

Answer / bathabile

DOL is a soft starter

Is This Answer Correct ?    1 Yes 12 No

Post New Answer

More Electrical Engineering Interview Questions

What is the Total Power generation Capacity in India at present ??

20 Answers   Bhel, College School Exams Tests, IBM, NTPC,


hi Is there any possibilities to find out the rotation of a shaft or something else by using electromagnectic waves or by IR rays.If s then can v change the dir., of rotation of the same by remotely?& how? plz dn't any1 say "NO r CAN'T"

0 Answers  


How we calculate the spacing between the conductors in 11,33KV lines?

3 Answers   NHPC,


What happens if the Capacitive Voltage Transformer Primary neutral is not earthed. There is a CVT between Transformer and source, and the CVT neutral of the transformer is not earthed, does it effect the transformer while charging or does it effect the transformer charging process.

1 Answers  


We have a 33/11kv switchyard having 12.5 MVA power transformer. We export & import power through this transformer. When we export power, the PF will be depend on GRID PF & when we import power the PF will be depend on our load PF. but the problem is that,when neither we export nor import but our 33KV vCB is in close position,our meter read the power factor 0.14 to 0.25 at that moment. So how can be we improve the power factor at that moment.

3 Answers  


Dear all, i completed M.E(Power Electronics & Drives) 2011 passed out having 78% so i need job in core side but i don't know how can i receive the calls from electrical companies and i uploaded my CV in naukri, times jobs etc.. In that iam not recieved any mails from good companies so give me best procedure plzzzzzzzzzzzzzzzzzzzzzzzz..... Thanks, K.Linga Reddy Email-id:-lingareddykmthm@gmail.com Ph no:-08015402078

1 Answers  


how to wiring it with contactor and timer together

0 Answers  


why high current produce in case of transformer when turns are internally gets shorted.

3 Answers   TCS,


what happen when transformer connect on dc supply.

5 Answers  


what are the advantages by using IGBT in VSC HVDC than thyristor in conventional HVDC

1 Answers   Bhel, Eskom,


We have laid the single core Armoured cable 7 nos ( 2 each phase & 1 neutral ) to cater our electrical load . the issue is though we have Glanded the cable both the end also givan the earthing to the panel both the end we are facing a heavy sparking at the gland side. what could be the reason.

12 Answers  


1)Why potential transformer primary site grounded? 2)can be loop between neutral & body for grounding? 3)What is the difference between ELCB &RCCB? 4)Why we use iron core in transformer insted of wooden core? 5)what is the principle of excitation? 6)Why we test the core balance test for transformer? 7)what is creepage?What is the creepage length for insulators at different voltages? 8)How much type of relays used for differential protection of generator,transformer & busbar protection?

5 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)