what is different the DOL Starter and Star Delta STARTER
Answer Posted / j.karthik
DOL Starter :
This starter is costwise cheap. it doesnot reduce the
starting current of the motor. The starting current of the
DOL starter is 6 to 7 times of the full load current. We can
use this starter for any higher kW range motors also even
6400kW motor.(In my working place using this DOL starter for
this 6400kW motor.
Note: for any standard cannot mentioned this much of the kW
motors only use in this type of starter nu..
Star/Delta Starter :
This starter is costwise higher. It can reduce the
starting current of the motor. The starter current of the
star/delta starter is 3 to 5 times of the full load current.
Generally in my working place this starter can be use above
75kW motors.
| Is This Answer Correct ? | 23 Yes | 24 No |
Post New Answer View All Answers
one electromagnet is called
How each of the following losses occur in d.c machines (i) copper (2)core (3) windage (4)friction please help me
whats the differece between Exd and Exe
what will be the maximum winding temperature of 6.6kv HT motor 450kw, Full load current 49A. 50Hz Frequency.
how you will decide the distance between the power transformer and its fencing
excitation limit of an excitor
How is the connection of the tap changer on the HV side been made?
How to calculate impedance volt in Transformer?
List out the different frequency domain specifications?
why 15 kw motor winding resistance is low then 5 kw motor winding resistance?
what is earth resistance? how to measured? and give values at power station and mcc area?
Dear Respected sir how to test ABB REX521 protection relay by relay tester.
When we use 3 terminal resistor?
Which contains in POLE ASSEMBLY of a 11KV Kirloskar-make SF6 (Model No-FP620A12)? Will u clarify with drawing?
if 2 coil of 1000W connect in series and 200 v is applied across it . then what is the total power of coil when coil have only resistive load .