if only one generator is running in droop mode parrallel
with grid and suddenly grid breaker off what will happen?
It will trip o/u freq or stay as it is? (urgent)
Answers were Sorted based on User's Feedback
Answer / suresh
It will iland mode but load to be as per generation extra
load to be disconnected immidiatly
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / kintoko adji
It's all depend on load and generator capacity, if load is
greater than generator capacity. If the load is much
greather than generator capacity (exam : 2 times of gen
capacity, it may trip because of under frequency, but
usually overload will be trip the generator CB first), but
if gen capacity is bigger than load, it will stay as it is.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / hamid
If this happen then turbine rpm and exactly frequency goes
up and depending on reaction of your control system to speed
variation , speed may be control or just lock out relay of
generator operate and turbine should not trip .
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mr.engineer
If you Have Island mode and you configuer it to switch from
deoop mode to Island mode at Grid tripping time, Your
system dose not effected by O/U freq.
Otherwise your system will trip due to underfrequency.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / ramesh
Hello Guys
The question has been asked without giving details what
this generator was doing. That is whether it was supplying
inhoue load with additional power drawn from grid or the
genrator was meeting inhouse load and exporting power.
The reply would depend on this.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / ismail yasin
genrator not alone together 4 steam turbine and all the
machine we are keeping droop mode all the time(with
parallel grid &islande mode.And we have separate load and
freq control systems. My question is when the machine
working alone and droop mode how will get freq reference?
and when parallel gird how will follow grid freq?
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mukhtar fouad
This is depend on what`s the mode of the grid? switching
off the mode of grid by operator to disconnect the grid
system mode,then the one genrator will continue running
without load and stay as it is (droop mode)
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / darshan thakur
When grid breaker trip at that time turbine comes in island mode
frequency goes to higher side,but if governor response as per
load through . When Grid trip governor will transfer from drop
mode to isochronous mode.
Is This Answer Correct ? | 0 Yes | 1 No |
Paralelling with grid mean your DG is running on stand by
mode or droop mode, your systems load is on grid. when grid
trips all load shifted on DG WITHOUT INTERRUPTION when grid
power comes check synchro. relay gives command again to DG
& it will again run on droop mode.
Is This Answer Correct ? | 1 Yes | 6 No |
Answer / vinod.t
when grid breaker trips..your generator is overloaded
suddenly frequency falls(47.75hz to 47hz depends on load)
and get trip on under frequency
Is This Answer Correct ? | 3 Yes | 9 No |
how to find the Motor,s insulation Power?
What is metering cubical? What is the use?
if we convert kw into Ampers,which one formula use by us,pls tell me?
what is meant by rotating magnetic filed
If the circuit breaker will not close or it will trip, what will you do?
how to calculate the minimum permissible limts of insulation resistance of switchyard equipments
WHAT IS DC COMPONENT IN CIRCUIT BREAKER?
What are various accuracy classes of CT(Current Transformer)
if we apply 1000ADC instead of 100ADC or We apply 50ADC instead of 100ADC,What will be happened in the test result value.Pl explain
ohms law is applicable for dc or ac current or for both??? explain it berifly??
how to male a d.c bettery to blow a 230v bulb?
what is G.O.D.S. ?