if only one generator is running in droop mode parrallel
with grid and suddenly grid breaker off what will happen?
It will trip o/u freq or stay as it is? (urgent)
Answer Posted / suresh
It will iland mode but load to be as per generation extra
load to be disconnected immidiatly
| Is This Answer Correct ? | 6 Yes | 0 No |
Post New Answer View All Answers
I have a relay contact rated at 220v dc which is supplied with a 24vdc from the panel,for it to trip the dampers(24vdc).What if the application of the relay changes so that it should work at its rated 220vdc then will it work at 24vdc supply given or any other consideration needs to be taken .....
How to choose size of the cable w.r.to current carrying capacity ...
why Induction Generators are not "Black start" ? and apart from WTGs where this types of generator are generally used?
what is auto re-closer?
Describe Non I.S. Earth System and why is it used?
What are the types of power in electrical power?
what is the difference between transformer,converter and transducer
if 6 earth pit value is 1.5 ohm then what should be the number of earth pit to make the value .8 ohm
what happened when we supply a dc current in dc motor?? can it worked properly?
what is a reactive power? what is the relation with power factor?
Why we do 2 types of earthing on transformer (ie:)body earthing & neutral earthing , what is function. I am going to install a oo kva transformer & 380 kva dg set what should the earthing value?
how to interlock 3 incomer-ACB,1 buscoupler ACB,... pls answer this question and if possible send me the ckt diagram..haifriends2910@gmail.com
In synchronous motor, how the field current is related to armature current..i know its inversely proportional..but concept wise...i was nt clear....pls help me...
What is the emf equation of a transformer?
what will happen if i connect 12 volt battery with 24 volt battery charger.