How to calculate the ups battery back up? give the formula.
Answers were Sorted based on User's Feedback
Answer / shailesh singh
Battey backup(va)=mah×v×n of battery/watt
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sathiyanarayanan
backup formula= KVA/DC LOW *POWER FACTOR
FOR EX:2 KVA/120 DC VOLT(SYSTEM VOLT)OUR MAINTAINED POWER
FACTOR (0.8 P.F),PER BATTERY=12V(DC LOW=10.8),HERE USING THE
SYSTEM VOLT=120V SO,10 BATTERIES-10*12=120V
DERIVATION : 2000/108*0.8
AH=14.81(APP.17 AH BATTERY) given 30 minutes backup
| Is This Answer Correct ? | 7 Yes | 8 No |
Answer / chetan singh
Battery Volt X No of Battery X Battery AH / Load in watt
| Is This Answer Correct ? | 4 Yes | 5 No |
Answer / mehboob
( Battery Voltage * AH Rating * Efficiency) / VA Rating = X
X * 60 = Estimated Run Time in Minutes
So let’s pretend we’re looking at a theoretical UPS unit that has the following specs:
VA Rating: 700
Battery Voltage: 12
AH: 9
Efficiency: 0.9 (90%)
When we plug those numbers into the equation we get the following:
( 12 * 9 * 0.9 ) / 700 = 0.139
0.139 * 60 = 8.3 minutes
| Is This Answer Correct ? | 0 Yes | 3 No |
what is diffrence between primary & secondry transformer?
what is neutral ground resistance relay? how it is helpful in protecting system?
For Eg a 30 kw motor at full load how much kw it takes And at no load how much KW it will take?
why we pefer the salient pole for synchronous motor ?
What is fault.?
2 Answers AngloGold Ashanti, MNC,
What are the different protection systems used to protect the transformer internally and externally?
My ups output shows 230 v between phase and neutral,but show zero between phase and earth.Is the system/installation is correct.If not what will be the possible reasons
What is slip in induction motor?
WHY WE USE CABLE JUNCTION AFTER BETWEEN TANSMISSION LINE AND TRANSFORMER
in how many ways we can make induction motor to run in reverse direction?
Is MV canble armour can be earthed at both ends?
How to calculate & connection of 900KVA generator 2 sets & load(1500A)? How to choose cable size and ACB size for this load & generator? please explain me detail. Regards, Mr.Han
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)