how can we can take BDV test in transformer?
Answers were Sorted based on User's Feedback
Answer / santosh kumar jha
BDV means break down voltage.
This is the test of di-electric strength of transformer oil.
The sample is taken in electrolysis pot and applied a
voltage diff between anode and cathode of the pot , the
diff between the two plate is 2.5 mm.At first we appling
the voltage diff gradually , the voltage near which the oil
looses its insulation property, that voltage is called BDV.
| Is This Answer Correct ? | 157 Yes | 7 No |
Answer / ilononurb
we can take the break down voltage of transformer oil by
using oil tester. Take oil sample of tr oil and put in to
the testing oil pot with the spere electrode of 2.5mm gap.
Applied gradually the voltage till the oil losses its
dielectric stenght. breakdown voltage will display to the
oiltester meter. As per IEC 156 Standards it should be
40kv.eff.
| Is This Answer Correct ? | 78 Yes | 8 No |
Answer / rahul sharma
BDV tests is used to test the dielectric strength of the
transformer.
A new transformer oil shol\uld have at least dielectric
strength of 39 KV as per british standards.
Transformer oil used are normally tested using ASTM D877-82
with the KV strength testing,using 1" electrode spaces 0.1"
apart & test voltage increased at 3000 volts\min until it
breaks down. The avg KV obtained after 8 trails is
considered the oil dielectric strength.
Using this test dielectric strength at 30KV & above is
considered good. Dielectric strength between 23 to 29 KV is
considered usable ,but requires filtering, below 23 KV
transformer oil should be replaced.
| Is This Answer Correct ? | 41 Yes | 8 No |
On TRANSFORMER OIL BREAK DOWN VOLTAGE test is carried out which is done on field while filling the oil in transformer. This process is also called oil filtration.
1.Take sample from top of Transformer before filtration.
2.The BDV of oil should withstood min 50 KV
3.The gap between the test electrodes sample to be 2.5mm maintained
4.At least 5 sample(top/bottom) should be checked separately while filtration.
5. The samples should withstand 50 kv for 1 min.
5. Take the average of all the samples timings.You will get value.
7.Procedure
a.Voltage should be gradually increased from 0.
b. At one point Flash will take place and that point is
termed as Bread down Voltage
| Is This Answer Correct ? | 26 Yes | 4 No |
Answer / s.anand
take sample before maintank bottom this coreact methode
| Is This Answer Correct ? | 2 Yes | 1 No |
What do you mean by transformation ratio of instrument transformer?
why the carbon brushes are used heat created rotating parts in eiectricity
IF DISTANCE IS 100METERS B/W AMP.METER AND CURRENT TRANSFORMER WHAT WILL BE AFFECT IN ACCURACY .METER CAN SHOWING ACCURATE CURRENT OR NOT IF NOT WHAT CAN I DO TO GET 100% ACCURACY.
-What is leakage current . how much leakage current is allowed.
what is balanced beam relay
identify the components of the tube light and explain how they function???wat is inside the fluroscent tube???how it works???
When the DG is running at the time we can connect to capacitor banK? why it is required or not
a)In a 3-phase 4-wire circuit, a circuit breaker is selected to protect the circuit whose highest fault level is 6.6 MVA. Determine the required minimum breaking capacity in kA. (Note: Covert 3-phase power in terms of kA to find answer.) b)Using the below, determine the required minimum making capacity in kA as a “peak value”. Rate breaking capacity (Icn) ka: Icn<= 1.5 Factor = 1.41 1.5
Why is earth connected to neutral on transfomer installations
what is earth fault relay 64T, why it is used in main Incomer and neutral CT of Transformer.
If NO contact of relay gets supply from other sources or other part of circuit and at a time relay coil activates,then current will flow in which direction & will it cause to damage relay??
Why don't connect earth wire to elcb?if earth fault occur,how will detect it
1 Answers TATA, Tata Communications, Telecommunications,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)