how can we can take BDV test in transformer?
Answers were Sorted based on User's Feedback
Answer / santosh kumar jha
BDV means break down voltage.
This is the test of di-electric strength of transformer oil.
The sample is taken in electrolysis pot and applied a
voltage diff between anode and cathode of the pot , the
diff between the two plate is 2.5 mm.At first we appling
the voltage diff gradually , the voltage near which the oil
looses its insulation property, that voltage is called BDV.
Is This Answer Correct ? | 157 Yes | 7 No |
Answer / ilononurb
we can take the break down voltage of transformer oil by
using oil tester. Take oil sample of tr oil and put in to
the testing oil pot with the spere electrode of 2.5mm gap.
Applied gradually the voltage till the oil losses its
dielectric stenght. breakdown voltage will display to the
oiltester meter. As per IEC 156 Standards it should be
40kv.eff.
Is This Answer Correct ? | 78 Yes | 8 No |
Answer / rahul sharma
BDV tests is used to test the dielectric strength of the
transformer.
A new transformer oil shol\uld have at least dielectric
strength of 39 KV as per british standards.
Transformer oil used are normally tested using ASTM D877-82
with the KV strength testing,using 1" electrode spaces 0.1"
apart & test voltage increased at 3000 volts\min until it
breaks down. The avg KV obtained after 8 trails is
considered the oil dielectric strength.
Using this test dielectric strength at 30KV & above is
considered good. Dielectric strength between 23 to 29 KV is
considered usable ,but requires filtering, below 23 KV
transformer oil should be replaced.
Is This Answer Correct ? | 41 Yes | 8 No |
On TRANSFORMER OIL BREAK DOWN VOLTAGE test is carried out which is done on field while filling the oil in transformer. This process is also called oil filtration.
1.Take sample from top of Transformer before filtration.
2.The BDV of oil should withstood min 50 KV
3.The gap between the test electrodes sample to be 2.5mm maintained
4.At least 5 sample(top/bottom) should be checked separately while filtration.
5. The samples should withstand 50 kv for 1 min.
5. Take the average of all the samples timings.You will get value.
7.Procedure
a.Voltage should be gradually increased from 0.
b. At one point Flash will take place and that point is
termed as Bread down Voltage
Is This Answer Correct ? | 26 Yes | 4 No |
Answer / s.anand
take sample before maintank bottom this coreact methode
Is This Answer Correct ? | 2 Yes | 1 No |
what is the difference between KW and KVA?
can any one help me for my ups inter view , list out few basic technical ups question with answer.
Write down the name of 2 lady Bir Pratin of Bangladesh
how to calculate the loss tangent of electrical cables
Type of cable insulation?
11 KV distribution system where neutral is produced ?
4 Answers ciss, TATA, Tata Motors,
Can 60 Hz transformer be used inplace of 50 hz transfromer?
Hello sir i m student of gtu .what is idp.
What is lighting kitts.
I am shobana from Chennai. I am having my personal interview on 19th Dec at Chennai.kindly mail me the questions to mail id shobana.shanthi@gmail.com
low voltage means how much voltage? extra low voltage means how much voltage? medium voltage means hos much voltage? high voltage means how much voltage? Ex: low voltage - 1volt to 240volt like this
Draw SLD feeding from the SS up to distribution board of the load, calculate cable size, breaker sizes, and meter for the following case: Ground Floor: electric room, pump room, 5 shops, each is 15 KW First Floor: 5 shops, each is 15 KW Second Floor: showroom 30 KW Service Loads: water pump 3 KW (3ph) , fire pump 3 KW (3ph), and one DB service 12 KW (3ph).