whycircuit breaker is not connected at the generator end
where the capacity of the generator is more say 60MW, 100MW
etc.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Gen side means usually 11 KV.The generator current at full
load will be very high for 60 MW( 52.5 x MVA A)for an
indoor breaker .Therefore , synchronization and tripping on
fault are done at EHT breaker which is of above 110 KV.For
any fault between the breaker and gen ,the master trip is
employed ,which trips the field breaker ,CB and the governor.
| Is This Answer Correct ? | 13 Yes | 5 No |
Due to following points
1)Transient Recovery Voltage (TRV)
2)Higher X/R value
3) Delayed current Zero
circuit breakers was not used after above 60 MW generators.
However please note that now full line of IEEE C37.013
qualified medium-voltage vacuum generator circuit breakers
for voltages up to 24 kV and generators up to 200 MW for
both indoor and outdoor applications are available in
market.
Please note that Circuit breakers applied to generator
switching applications are subject to conditions quite
different than those of a normal distribution circuit
breaker used in industrial, commerical and utility systems.
Distribution circuit breakers, whether of the outdoor
substation type or of the drawout type for use in metal-
clad switchgear, conform to IEEE C37.04 (basis of ratings),
IEEE C37.06 (preferred ratings), IEEE C37.09 (testing) and
IEEE C37.10 (application.)
| Is This Answer Correct ? | 5 Yes | 6 No |
Which circuit breaker arc quenching time is low AC or DC breaker?
how i calculate the syncrones generator NGR resistance .if we have a 6mw generator line voltage of generator 11kv also line current 393.3 ampere.
What is fault level?How it is calculated and how it is Expressed?
Brushes are placed at magnetically neutral axis,when brushes reach that point,the armature conductor gets shorted,but it can be seen that the dc supply is also shorted,wont that get damage? help me plz
what is the maximum demand how it is defined
what is the function of breather in a transformer
29 Answers Areva, Bhel, RKM Powergen, Vijai Electricals,
how calculated Transformer losses.
What is VFD, and how its work
Why do we need a separate control desk & PLC control panel in Boiler plant or coal handling plant? Can we provide cost effective Control desk cum PLC panel. Is there is an specific need for control desk.. kindly advice.
what is the difference between high impedance REF & REF, same high impedance differential protection & differential protection for Power transformer?
checking procedure of capacitor based motors.used in fans etc?
can we use transformer for 70 Hz?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)